[EnergyPlus_Support] Re: Fwd: Central Heat Production vs terminal units
Thanks.
I based my adpated model on that Example File, and I've checked again
now... I think that node connections and the like are correct...
I get some warnings about freezing possibility, but other than that,
it seems OK... except that the Heat Pump DX Coil gives a lot more
energy than is being used by the demand side coils.
I'll keep trying to find out the bug, I guess...
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> Look at the example file HeatPumpWaterHeater.idf. In your file,
hook up
> the plant loop to the USE SIDE nodes in the WaterHeater:Mixed
object.
> Just use a 1 for the use side effectiveness value.
>
> HEAT PUMP:WATER HEATER,
> Zone5HeatPumpWaterHeater,!- Heat Pump Name
> HeatPumpWaterHeaterSch, !- Availability Schedule Name
> HPWHTempSch, !- Heat Pump Compressor Set Point
> Temperature Schedule Name
> 2.0, !- Dead Band Temperature Difference
{deltaC}
> HPWHWaterInletNode, !- Condenser Water Inlet Node Name
> HPWHWaterOutletNode, !- Condenser Water Outlet Node Name
> autocalculate, !- Condenser Water Volumetric Flow
Rate {m3/s}
> autocalculate, !- Evaporator Air Volumetric Flow Rate
{m3/s}
> Zone and Outdoor Air, !- Inlet Air Configuration
> HPWHAirOutletNode, !- Heat Pump Air Inlet Node Name
> HPWHAirInletNode, !- Heat Pump Air Outlet Node Name
> HPWHOutdoorAirInletNode, !- Outside Air Node Name
> HPWHExhaustAirOutletNode,!- Exhaust Air Node Name
> , !- Inlet Air Temperature Schedule Name
> , !- Inlet Air Humidity Schedule Name
> SPACE5-1, !- Inlet Air Zone Name
> Water Heater:Mixed, !- Water Heater Tank Type
> HPWHTank, !- Water Heater Tank Name
> , !- Water Heater Tank Use Side Inlet
Node Name
> , !- Water Heater Tank Use Side Outlet
Node Name
> Coil:DX:HeatPumpWaterHeater, !- DX Coil Type
> HPWHDXCoil, !- DX Coil Name
> 5.0, !- Minimum Inlet Air Temperature for
Heat
> Pump Compressor Operation {C}
> Zone, !- Compressor Location
> , !- Compressor Ambient Temperature
Schedule Name
> Fan:Simple:OnOff, !- Fan Type
> HPWHFan, !- Fan Name
> Draw Through, !- Fan Placement
> 15.0, !- On-Cycle Parasitic Electric Load {W}
> 5.0, !- Off-Cycle Parasitic Electric Load
{W}
> Zone, !- Parasitic Heat Rejection Location
> HPWHInletAirMixerNode, !- Inlet Air Mixer Node Name
> HPWHOutletAirSplitterNode, !- Outlet Air Splitter Node Name
> HPWHMixerInletAirSch; !- Inlet Air Mixer Schedule Name
>
>
> WATER HEATER:MIXED,
> HPWHTank, !- Name
> 0.3785, !- Tank Volume {m3}
> Hot Water Setpoint Temp Schedule, !- Setpoint Temperature
Schedule
> 2.0, !- Deadband Temperature Difference
{deltaC}
> 82.2222, !- Maximum Temperature Limit {C}
> CYCLE, !- Heater Control Type
> 5000, !- Heater Maximum Capacity {W}
> 0, !- Heater Minimum Capacity {W}
> , !- Heater Ignition Minimum Flow Rate
{m3/s}
> , !- Heater Ignition Delay {s}
> ELECTRICITY, !- Heater Fuel Type
> 0.95, !- Heater Thermal Efficiency
> , !- Part Load Factor Curve
> 10, !- Off-Cycle Parasitic Fuel
Consumption
> Rate {W}
> ELECTRICITY, !- Off-Cycle Parasitic Fuel Type
> 0, !- Off-Cycle Parasitic Heat Fraction
To Tank
> 30, !- On-Cycle Parasitic Fuel Consumption
Rate {W}
> ELECTRICITY, !- On-Cycle Parasitic Fuel Type
> 0, !- On-Cycle Parasitic Heat Fraction To
Tank
> ZONE, !- Ambient Temperature Indicator
> , !- Ambient Temperature Schedule
> SPACE5-1, !- Ambient Temperature Zone
> , !- Ambient Temperature Outside Air Node
> 2.0, !- Off-Cycle Loss Coefficient To
Ambient
> Temperature {W/K}
> 1.0, !- Off-Cycle Loss Fraction To Zone
> 2.0, !- On-Cycle Loss Coefficient To
Ambient
> Temperature {W/K}
> 1.0, !- On-Cycle Loss Fraction To Zone
> 0.00379, !- Peak Volumetric Use Flow Rate {m3/s}
> Hot Water Demand Schedule, !- Use Flow Rate Fraction Schedule
> , !- Cold Water Supply Temperature
Schedule
> , !- Use Side Inlet Node
> , !- Use Side Outlet Node
> , !- Use Side Effectiveness
> HPWHWaterOutletNode, !- Source Side Inlet Node
> HPWHWaterInletNode, !- Source Side Outlet Node
> 0.95; !- Source Side Effectiveness
>
>
> COIL:DX:HEATPUMPWATERHEATER,
> HPWHDXCoil, !- Coil Name
> 4000.0, !- Heating Capacity {W}
> 3.2, !- Rated COP {W/W}
> 0.6956, !- Rated SHR (gross)
> 29.44, !- Rated Evaporator Inlet Air Dry-Bulb
> Temperature {C}
> 22.22, !- Rated Evaporator Inlet Air Wet-Bulb
> Temperature {C}
> 55.72, !- Rated Condenser Inlet Water
Temperature {C}
> autocalculate, !- Rated Evaporator Air Volumetric
Flow
> Rate {m3/s}
> autocalculate, !- Rated Condenser Water Volumetric
Flow
> Rate {m3/s}
> No, !- Evaporator Fan Power Included in
Rated COP
> No, !- Condenser Pump Power Included in
Rated COP
> No, !- Condenser Pump Heat Included in
Rated
> Heating Capacity and Rated COP
> 150.0, !- Condenser Water Pump Power {W}
> 0.1, !- Fraction of Condenser Pump Heat to
Water
> HPWHInletAirMixerNode, !- Evaporator Air Inlet Node Name
> HPWHDXCoilAirOutletNode, !- Evaporator Air Outlet Node Name
> HPWHWaterInletNode, !- Condenser Water Inlet Node Name
> HPWHWaterOutletNode, !- Condenser Water Outlet Node Name
> 100.0, !- Crankcase Heater Capacity {W}
> 5.0, !- Maximum Ambient Temperature for
> Crankcase Heater Operation {C}
> wet-bulb temperature, !- Evaporator Air Temperature Type for
> Curve Objects
> HPWHHeatingCapFTemp, !- Heating Capacity Modifier Curve
Name
> (function of temperature)
> , !- Heating Capacity Modifier Curve
Name
> (function of air flow fraction)
> , !- Heating Capacity Modifier Curve
Name
> (function of water flow fraction)
> HPWHHeatingCOPFTemp, !- Heating COP Modifier Curve Name
> (function of temperature)
> , !- Heating COP Modifier Curve Name
> (function of air flow fraction)
> , !- Heating COP Modifier Curve Name
> (function of water flow fraction)
> HPWHPLFFPLR; !- Part Load Fraction Correlation Name
> (function of part load ratio)
>
> anarui.oliveira wrote:
> >
> > Maybe this additional information helps:
> >
> > ...I started out with a model of a boiler created with Compact
HVAC,
> > and then expanded it and substituted the boiler by the Heat Pump
Water
> > Heater.
> > The expanded model with the boiler works fine... so I guess I
missed
> > something when adapting it to a model with a heat pump?...
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "anarui.oliveira"
> > <anarui.oliveira@> wrote:
> >
> > Hi everyone.
> >
> > I modelled a system with a central Heat pump (air-to-water),
producing
> > heat for a hot water loop serving 3 Air Treatment Units and some
> > terminal unit ventilators, but the thermal heating rate/energy
produced
> > by the central heat pump is much (2-3 times) higher than the sum
of the
> > heating rates/energy of all the coils in the ATUs and terminal
units...
> > It seems as if the control os this central unit is not performing
> > properly, but I can't figure out why...
> >
> > Could anyone help?
> >
> > Thanks in advance,
> > Ana Rui.
> >
> > --- End forwarded message ---
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/