Re: [EnergyPlus_Support] Fancoil units



Just define 2 zone inlet nodes and use 1 inlet node for each. See the 
Controlled Zone Equip Configuration object. Use a node list to define 
more than one node for inlet or exhaust nodes.

CONTROLLED ZONE EQUIP CONFIGURATION,
Zone 1,  !- Zone Name
,  !- List Name: Zone Equipment
Zone 1 Inlet Nodes,    !- Node List or Node Name: Zone Air Inlet Node(s)
,  !- Node List or Node Name: Zone Air Exhaust Node(s)
,  !- Zone Air Node Name
;  !- Zone Return Air Node Name

NODE LIST,
Zone 1 Inlet Nodes,    !- Node List Name
Zone 1 Inlet Node 1,   !- Node_ID_1
Zone 1 Inlet Node 2,   !- Node_ID_2


aymericnovel wrote:
>
> Hi,
>
> I am a bit new in using E+ so my question my sounds simple:
>
> When modelling fancoil unit system, the inlet node is the zone exhaust
> node and the outlet node is the zone inlet node.
> Fine, but I want my fresh air coming from AHU to arrive in the zone too
> and in my case the fancoil is not a terminal unit but is within the
> zone. Is it possible to connect both to the zone inlet node?
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/