[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] weather file



Yes, I found it. Many thanks for you.
Eman

--- On Thu, 9/4/08, Crawley, Drury <Drury.Crawley@xxxxxxxxxx> wrote:
From: Crawley, Drury <Drury.Crawley@xxxxxxxxxx>
Subject: RE: [EnergyPlus_Support] weather file
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Date: Thursday, September 4, 2008, 7:53 PM

Look on the EnergyPlus_Support YahooGroup web site:


From: EnergyPlus_Support@ yahoogroups. com [mailto:EnergyPlus_ Support@yahoogro ups.com] On Behalf Of Eman Abd El-Hakim Tora
Sent: Thursday, September 04, 2008 1:33 PM
To: EnergyPlus_Support@ yahoogroups. com
Subject: [EnergyPlus_ Support] weather file


Hello
I need the weather file of  Qatar, Doha. Please, if you have it or a guide to it let me know.
Thank you very much.
Eman
 
 
--- On Thu, 9/4/08, jim_mcnally <jim_mcnally@ yahoo.com> wrote:
From: jim_mcnally <jim_mcnally@ yahoo.com>
Subject: [EnergyPlus_ Support] Heat Recovery Option for Compact HVAC: Unitary apprears to not work
To: EnergyPlus_Support@ yahoogroups. com
Date: Thursday, September 4, 2008, 7:01 PM

Hi,
I have been trying to simulate a unitary HVAC device with a heat
recovery module. I am using the Compact:Unitary equipment simulation.
The heat recovery option does not materially change the energy use
results.
A one zone building with one rooftop unit is my quick running test
model. The compact unitary part is given below.

Am I missing something?
Regards,
Jim McNally

****** COMPACT UNITARY PART OF EP MODEL ******
!- =========== ALL OBJECTS IN CLASS: COMPACT HVAC:THERMOSTAT
===========

COMPACT HVAC:THERMOSTAT,
TSTAT-ADM_1FL, !- Thermostat Name
, !- Thermostat Heating Setpoint Schedule
22.2222228109101, !- Thermostat Constant Heating Setpoint
{C}
, !- Thermostat Cooling Setpoint Schedule
22.7777783811828; !- Thermostat Constant Cooling Setpoint
{C}

COMPACT HVAC:THERMOSTAT,
TSTAT-CENTER, !- Thermostat Name
ofc_HTG-Temp_ SCHED, !- Thermostat Heating Setpoint Schedule
, !- Thermostat Constant Heating Setpoint
{C}
ofc_CLG-Temp_ SCHED, !- Thermostat Cooling Setpoint Schedule
; !- Thermostat Constant Cooling Setpoint
{C}

COMPACT HVAC:THERMOSTAT,
TSTAT-RESIDENT, !- Thermostat Name
Resident_HTG- Temp_SCHED, !- Thermostat Heating Setpoint Schedule
, !- Thermostat Constant Heating Setpoint
{C}
RESIDENT_CLG- Temp_SCHED, !- Thermostat Cooling Setpoint Schedule
; !- Thermostat Constant Cooling Setpoint
{C}

!- =========== ALL OBJECTS IN CLASS: COMPACT HVAC:ZONE:UNITARY
===========

COMPACT HVAC:ZONE:UNITARY,
5F92EB, !- Zone Name
S-1, !- Air Handling System Name
TSTAT-ADM_1FL, !- Thermostat Name
9.44000119843765, !- Zone Supply Air Max Flow Rate {m3/s}
flow/zone, !- Zone Outside Air Flow Type
0, !- Zone Outside Air Flow Rate {m3/s}
, !- Zone Supply Plenum Name
; !- Zone Return Plenum Name

!- =========== ALL OBJECTS IN CLASS: COMPACT HVAC:SYSTEM: UNITARY
===========

COMPACT HVAC:SYSTEM: UNITARY,
S-1, !- Air Handling System Name
, !- System Availability Schedule
5F92EB, !- Control Zone Name or Thermostat
Location
9.44000119843765, !- Supply Fan Max Flow Rate {m3/s}
, !- Supply Fan Operating Mode
0.7, !- Supply Fan Total Efficiency
871.8113780762, !- Supply Fan Delta Pressure {Pa}
0.9, !- Supply Fan Motor Efficiency
1, !- Supply Fan Motor in Air Stream
Fraction
Single-speed DX, !- Cooling Coil Type
, !- Cooling Coil Availability Schedule
autosize, !- Cooling Coil Capacity {W}
autosize, !- Cooling Coil Rated SHR
3, !- Cooling Coil Rated COP
Gas, !- Heating Coil Type
, !- Heating Coil Availability Schedule
autosize, !- Heating Coil Capacity {W}
0.8, !- Gas Heating Coil Efficiency
, !- Gas Heating Coil Parasitic Electric
Load {W}
9.44000119843765, !- Maximum Outside Air Flow Rate {m3/s}
9.44000119843765, !- Minimum Outside Air Flow Rate {m3/s}
, !- Minimum Outside Air Schedule Name
None, !- Economizer Type
NO LOCKOUT, !- Economizer Lockout
, !- Economizer Upper Temperature Limit {C}
, !- Economizer Lower Temperature Limit {C}
, !- Economizer Upper Enthalpy Limit {J/kg}
, !- Supply Plenum Name
, !- Return Plenum Name
Blow Through, !- Supply Fan Placement
Cycle On Control Zone, !- Night Cycle Control
5F92EB, !- Night Cycle Control Zone Name
Sensible, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness
0.65; !- Latent Heat Recovery Effectiveness



__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___