So you want the ventilation to control the CO2, but at times you want 
the ventilation rate to increase to satisfy the temperature. The only 
way I can think to do this is to run 2 simulations, the 1st with only 
mechanical ventilation to satisfy the occupancy/material emissions and 
the 2nd to satisfy only the zone temperature. Then take the 2 
ventilation rates and calculate a new "minimum outside air schedule" 
which is the maximum ventilation rate from the 2 simulations. See 
documentation for Schedule:File:Comma.

sartori_igor wrote:
>
> Hei all,
>
> I have a problem understanding how to implement a specific ventilation
> control in E+.
>
> You will find the description of the problem in the file:
>
> "Ventilation control_E+ yahoo group.doc"
> (under the menu "Files")
>
> please take a look to it, it is just 1 figure and 1 formula, nothing
> scary to understand! (but perhaps to implement?)
>
> Thanks very much to anyone who would have suggestions or comments
> about this.
>
> Igor
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/