[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: DX:coil:heatpumpwaterheater, Minimum Evaporator Temperature



Yes, we have answered this before. The problem is that if the air 
entering the DX cooling coil is less than about 5C, the coil will freeze 
up. There is currently no frost control in the heat pump water heater 
model. Usually this type of water heater would be protected from the 
environment in a mechanical room.

JV Dirkes II wrote:
>
> This sounds failiar. Have you checked previous posts? I think this
> was a topic about 6 months ago.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>, "aymericnovel"
> <aymericnovel@...> wrote:
> >
> > Hi all,
> >
> > I have been modelling a building with an air to water heat pump as
> > heating plant. I used the object DX:COIL:HEATPUMPWATERHEATER, which is
> > then connected to a WATERHEATER:MIXED (tank) and a FAN:ONOFF.
> >
> > In the principle it works well BUT: The heat pump does not work if the
> > air temperature at the evaporator is less than 5°C!! Is there any way
> > to make it work at less than 5°C so that my heat pump produces heat
> > during the whole winter even if COP is low?
> >
> > If this is not possible, is there another way (other object) to
> > simulate this kind of heat pump?
> >
> > Thanks for your help,
> > Best regards,
> > Aymeric
> >
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/