Re: [EnergyPlus_Support] Re: Outside Air Mixing Box



Make the OA flow rate equal to the rated volumetric flow of the air loop 
This will make the recirc air = 0.

Elreq wrote:
>
> I already did this. I set the min OA equal to the max OA, but I still
> see that the recirculation is active in order to keep the rated
> volumetric flow of the air loop always constant.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>, amit bhansali
> <amitbhansali2003@...> wrote:
> >
> > Hi,
> > If you are using the new version of Energyplus , you would see two
> schedules added in the object named Min OAflow Sched and Max OAflow
> Sched, and give all schedule value for these as 1, so the system
> would operate on 100% outside air.
> >
> > Amit Bhansali
> > Vice President, ASHRAE Student Branch
> > Research Assistant,Mechanical and Aerospace Engineering Department
> > Oklahoma State University
> >
> >
> >
> > ----- Original Message ----
> > From: lee_ching_hei <cheung5407@...>
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > Sent: Tuesday, 7 October, 2008 8:44:02 AM
> > Subject: [EnergyPlus_Support] Re: Outside Air Mixing Box
> >
> >
> > Dear all,
> > I am trying to add an air economizer and I met the same problem. I
> > don't know how to control the system with 100% fresh air (without
> > mixing with circulated air). I hope that there is someone who can help
> > us.
> >
> > Gary
> >
> > --- In EnergyPlus_Support@ yahoogroups. com, "Elreq" <tolteca33@ ..>
> > wrote:
> > >
> > > Hello,
> > >
> > > Does anybody know how can I make that all the return air entering the
> > > mixing box is completely passed to the Relief air stream node? In
> > > other words, I do not want any recirculation of air, so I want the
> > > damper of the mixing box to be closed. I am trying to find a way but I
> > > still cant manage how to do it.
> > >
> > > Thanks in advance.
> > >
> > > Santiago
> > >
> >
> >
> >
> >
> > Download prohibited? No problem. CHAT from any browser,
> without download. Go to http://in..webmessenger.yahoo.com/ 
> <http://in..webmessenger.yahoo.com/>
> >
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/