Re: [EnergyPlus_Support] Enquires- urgent



In addition to reading the documentation, see example file 
5ZoneWaterCooled_HighRHControl if you are using a chilled water coil 
(you need to add a Set Point Manager:Single Zone Max Hum in addition to 
the thermostat and humidistat) or FurnaceWithDXSystemRHControl for a 
direct-expansion (DX) cooling coil (only a thermostat and humidistat are 
required).

Sze Hung Lee wrote:
> Dear sir,
> I would like to know to how to make both humidity and temperature 
> control of a zone using a conventional constant air volume system , 
> CAV system. Since I have made both the zone humidist and the zone 
> thermostat control of bith the humidity and the temperature, the 
> simulation results indicate that there are no control on the humidity 
> level. Whether I can set the control of cooling coil with both 
> humidity and temperature is possible; if possible, can you teach me 
> how to do so?
> Best regards
> Timothy Lee 
>
> _______________________________________
> YM - 離線訊息
> 就算你沒有上網,你的朋友仍可以留下訊息給你,當你上網時就能立即看到,任 
> 何說話都冇走失。
> http://messenger.yahoo.com.hk
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/