[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Heating Coil is not responding to thermostat



You should be using a Set Point Manager:Single Zone Heating object to 
set the heating coil outlet node set point. Similarly, a Set Point 
Manager:Single Zone Cooling object should be used to set the cooling 
coil outlet node set point. You will have to pick a zone for the 
thermostat. The other option is to use air loop cooling and terminal 
unit heating if you want thermostats in all zones.

Elreq wrote:
>
> Dear Forum, I have the following problem,
>
> I have a building office, with 3 zones, North zone, south zone and a
> core zone. I have heating a setpoint of 21 C and cooling of 24 C.
>
> The problem is that the heating coil starts to provide heated air to
> the zones, but it continues delivering even if the temperatures in the
> zones are higher than 21 C. So it seems that is not respecting the
> setpoint temperatures of the zones.
>
> Any help or suggestion greatly appreciated.
>
> Santiago
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/