Re: [EnergyPlus_Support] Averaging thermostat?
That one's a keeper. E+ is not able to do that right now (up through V3)
and I can't think of a way to trick the simulation. The only thing you
can really do is balance the air flow to each zone so their temperatures
are as close as possible.
careym.cosmaj wrote:
>
> Just a quick question, and it may be totally dumb, there does not
> appear to be an Set Point Manager:Averaging.
>
> It may be possible to command setpoint from a node downstream of a
> ZONE:MIXER object in the return air stream, however this will not get
> me the average zone temperature.
>
> When I have multiple zones connected to a single system I can use
> either Set Point Manager:Warmest or Set Point Manager:SingleZone
> Cooling allowing me to control from the warmest zone or the one I
> specify but not allowing an average to be taken into account.
>
> Is there some trickery than can be done with a Set Point Manager:Mixed
> Air where it gets a little abused by pretending two zones are a fan or
> something similar to get an average in the current time step?
>
> Thanks for any suggestions.
>
> Regards,
>
> Mark Carey
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/