Re: [EnergyPlus_Support] controlling doas



I think you still need the mixing box, even though it is unused.

There is no way currently to vary the primary air system flow with a 
schedule, with OA requirements,
or any other way. It is either constant flow, or VAV with the flow 
determined by the zone loads.
One exception is a variable flow, variable temperature set point 
manager. But that is irrelevant
for your needs.

Fred Buhl

Alan Jackson wrote:
> so in my attempt to model chilld beams i have used the FPIU example
> file to merge with my surface geometry, scheduling and such. That has
> been successful. 
>
> I am looking to have the OA = Primary Air Loop volumeflowrate and be
> controlled based on occupancy and OA/person. Essentially the mixing
> box becomes obsolete. Two things, 1) i see the ability to have the
> Primary Air be fixed, but is it possible to be fixed to the OA needs
> 2)should i remove the mixing box all together as it becomes uneeded,
> with the intention to aid a double wheel later on for energy recovery.
>
> look forward to everyone's help.
>
> -
> alan
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   

------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/