Hi I've done this before in the following
way: In the condenser loop where you would usually put your cooling tower
(under the CondenserEquipmentList object), substitute in a DistrictCooling
object (formerly known as PURCHASED:CHILLED WATER in earlier versions of E+).
Then put a SetpointManager:Scheduled object on the condenser loop. Point
it to control the outlet node of the supply-side condenser loop. Finally
setup the schedule on the SetpointManager to match the temperature of the sea
water—I had monthly average values. To bypass the chiller completely for
waterside economizing, you'll need to use a HeatExchanger:Hydronic object (formerly
HEAT EXCHANGER:HYDRONIC:FREE COOLING ) or one of the other HeatExchanger:XYZ
objects to connect the plant loop to the condenser loop. Check out the example files included with
E+ for illustrations of how to setup a condenser loop, setpoint manager, and
heat exchangers. If the sea water temperatures ever go
below 5 C you'll also need to hack the Energy+.idd file to change the
CondenserLoop definition so that Minimum Loop Temperature is allowed to go
colder. Good luck, P From: Dear Forum, The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.