[EnergyPlus_Support] Re: Sea Water Air Conditioning System



Dear Peter,

I have followed your suggestion but I found out that the object
Purchased Cooling is not allowed to be in the Condenser Equipment
list. How did you manage to include it?

Regards,
Santiago
>
>  
> 
> Hi Santiago,
> 
>  
> 
> I've done this before in the following way:  In the condenser loop where
> you would usually put your cooling tower (under the
> CondenserEquipmentList object), substitute in a DistrictCooling object
> (formerly known as PURCHASED:CHILLED WATER in earlier versions of E+).
> Then put a SetpointManager:Scheduled object on the condenser loop.
> Point it to control the outlet node of the supply-side condenser loop.
> Finally setup the schedule on the SetpointManager to match the
> temperature of the sea water-I had monthly average values.
> 
>  
> 
> To bypass the chiller completely for waterside economizing, you'll need
> to use a HeatExchanger:Hydronic object (formerly HEAT
> EXCHANGER:HYDRONIC:FREE COOLING ) or one of the other HeatExchanger:XYZ
> objects to connect the plant loop to the condenser loop.  
> 
>  
> 
> Check out the example files included with E+ for illustrations of how to
> setup a condenser loop, setpoint manager, and heat exchangers.  
> 
>  
> 
> If the sea water temperatures ever go below 5 C you'll also need to hack
> the Energy+.idd file to change the CondenserLoop definition so that
> Minimum Loop Temperature is allowed to go colder.  
> 
>  
> 
> Good luck,
> 
> P
> 
>  
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Elreq
> Sent: Monday, December 01, 2008 8:42 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Sea Water Air Conditioning System
> 
>  
> 
> Dear Forum,
> 
> I was wondering if anyone has tried to use E+ to simulate a Sea Water
> Air conditioning system. I think that the Ground Heat Exchanger: Pond
> could be used as an approximation.
> 
> Any suggestions or ideas?
> 
> Thanks 
> 
> Santiago
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/