[EnergyPlus_Support] Rated air volume flow rate per watt of rated total cooling capacity out of range



Dear All,
 
I am trying to simulate a thermal zone with Compact HVAC: Zone: PTHP by entering the data from the manufacturer catalogue: 56000 W rated total cooling capacity (gross) and 2,0 m3/s rated air volume flow rate.
But, when I run the simulation, comes up a severe error as listed below and the program stops running.
 
Severe  ** Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "2O_PAV._ZONA1 PTHP COOLING COIL": Rated air volume flow rate per watt of rated total cooling capacity is out of range. See Input-Output Reference Manual for valid range.
 
According to manual, the range is between 0,00004027 and 0,0006041 m3/s/W.
 
The value of the manufacturer catalogue is 0,00003571 m3/s/W, below the Energyplus range. 
 
Is there some way to "bypass" this error or to modify these limits in the program?
 
Please, I would appreciate if someone could help me in this question.
 
Thank you.
 
Adriano
__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___