|
Dear All,
I am trying to simulate a thermal zone
with Compact HVAC: Zone: PTHP by entering the data
from the manufacturer catalogue: 56000 W rated total
cooling capacity (gross) and 2,0 m3/s rated air volume flow
rate.
But, when I run the simulation, comes up
a severe error as listed below and the program stops
running.
Severe ** Sizing:
COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "2O_PAV._ZONA1 PTHP COOLING COIL": Rated
air volume flow rate per watt of rated total cooling capacity is out of range.
See Input-Output Reference Manual for valid range.
According to manual, the range is
between 0,00004027 and 0,0006041 m3/s/W.
The value of the manufacturer
catalogue is 0,00003571 m3/s/W, below the Energyplus range.
Is there some way to "bypass" this error or to
modify these limits in the program?
Please, I would appreciate if someone could help me
in this question.
Thank you.
Adriano
__._,_.___
The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |