Would you also please provide the manufacturer name and web site link so
the E+ team can look at this data? Thank you.
Edwin Lee wrote:
>
>
> Does the simulation continue to run fine? Even though this is a
> severe error, I don't think it will cause the simulation to cease, it
> is just letting you know that this was encountered during the sizing
> runs as it moves ahead with the simulation.
>
> Edwin
>
> On Wed, Dec 3, 2008 at 11:33 AM, Adriano Carotenuto
> <adriano.carotenuto@xxxxxxxxxxxx
> <mailto:adriano.carotenuto@xxxxxxxxxxxx>> wrote:
>
> Dear All,
>
> I am trying to simulate a thermal zone with Compact HVAC: Zone:
> PTHP by entering the data from the manufacturer catalogue: 56000 W
> rated total cooling capacity (gross) and 2,0 m3/s rated air
> volume flow rate.
> But, when I run the simulation, comes up a severe error as listed
> below and the program stops running.
>
> Severe ** Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL
> "2O_PAV._ZONA1 PTHP COOLING COIL": Rated air volume flow rate per
> watt of rated total cooling capacity is out of range. See
> Input-Output Reference Manual for valid range.
>
> According to manual, the range is between 0,00004027 and 0,0006041
> m3/s/W.
>
> The value of the manufacturer catalogue is 0,00003571 m3/s/W,
> below the Energyplus range.
>
> Is there some way to "bypass" this error or to modify these limits
> in the program?
>
> Please, I would appreciate if someone could help me in this question.
>
> Thank you.
>
> Adriano
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/