Eric,
If measured solar data is available, then by all
means you should get it.
However, make sure first that the weather bureau is
indeed providing measured
radiation, and not calculating it from other
parameters, since recording solar
radiation is not standard operating practice for
typical weather stations. If
you can get measured solar, consider yourself very
lucky.
The only critical measured radiation values are the
global horizontal, and the direct
normal radiation. Everything else can be calculated
from these two.
If your weather bureau can provide only the
global horizontal, you will need to use
a model to do the direct/diffuse split.
The DOE-2 *.BIN file contains just the global horizontal and direct normal.
I'm surprised you're thinking of creating an EPW
and then translating it to BIN.
I've been doing the opposite - create first
a "bare bones" *.BIN file, and then
filling out the additional data needed for an EPW.
Joe Huang
White Box Technologies, Inc.
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.