Since I suppose your question is not necessarily exclusive to E+, I just 
downloaded some TMY3 files to double check. Sure enough the illuminance 
data are wrong by a factor of 100 for the 2-31 Jan period. The zenith 
luminance data are wrong too, but by a different factor, 10 or so.

Chris

> Hello, at the NREL link to the TMY3 source data:
>
> http://rredc.nrel.gov/solar/old_data/nsrdb/1991-2005/tmy3/
>
> I saw this notice:
>
> 20-AUG-2008 NOTICE
>
> All illuminance and luminance values for all TMY3 stations from January 
> 2 to 31 should be multiplied by 100 to obtain the correct units of Lux 
> and Candela per square meter. NREL will be posting a corrected data set 
> in the near future. 
>
>
> Does this mean that the January illuminance and luminance values in the 
> TMY3 EPW files are incorrect?
>
>
>
>   


-- 
Chris A. Gueymard, PhD
Solar Consulting Services
P.O. Box 392
Colebrook, NH 03576, USA
Tel. (603) 237-8550
Fax  (603) 237-5314
http://www.SolarConsultingServices.com


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/