[EnergyPlus_Support] Re: one strange problem about weather data
Thanks a lot.
Problem solved.
yeah, it's the problem of time step..
> The reason is that EnergyPlus uses sub-hourly time steps and the
data
> are "averaged" over the reporting frequency.
>
> Change the number of timesteps per hour to 1 (ref Timestep object)
and
> the minimum system timestep to 0 (ref ConvergenceLimits object) and
try
> the comparison again.
>
> Timestep, 1; !- Number of Timesteps per Hour
> ConvergenceLimits, 0; !- Minimum System Timestep
>
> Let us know if you still find difference in the weather file data..
>
> hvacgeshen516 wrote:
> >
> > Problem description:
> > I downloaded one weather data from www.energyplus.gov
> >
> > 1. I transfer it from epw to csv format;
> > 2. I use this epw to do simulation and get output about outdoor
dry bulb.
> >
> > however, results are: outdoor dry bulb from 1 and 2 are
different...
> >
> > who know why? thanks
> >
> > I am still trying to find the reason..
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/