Thank you for quickly answering. It is already some considerations I
will take care of.
Now, I know the cooling coil is sized by E+ based on sensible load.
My technical question is more about: Can it be sized by changing the
blown air temperature instead of the airflow rate? or does the E+
code leave no choice for that?
I mean now it keeps blowing air at 13.5°C in the zone but it reduces
airflow rate from 0.08kg/s to 0.05kg/s to reduce cooling capacity.
Could it be more like keeping airflow rate at 0.08kg/s and blowing
air at 15°C or 16°C?
Regards,
Aymeric
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II"
<jvd2pe@...> wrote:
>
> Dear Aymeric,
>
> Some general considerations:
>
> Split system DX systems always have difficulty controlling
humidity; the
> thermostat senses only temperature in most cases. In addition, the
> cooling coil is not designed or intended for high latent loads
> (generally a sensible heat ratio of ~0.7 is expected). The fact
that
> the compressor cycles on and off compounds the humidity control
> problems, since no humidity gets removed during an "off" cycle. In
> fact, moisture on the cooling coil can even get re-absorbed if the
fan
> continues to operate while the compressor is off.
>
> Your system gets sized by E+ according to sensible load, not latent
> load. When you reduce the sensible load, but latent loads remain
> unchanged, the space humidity will rise because the DX coil
> (correctly) canot handle the higher sensible heat ratio.
>
> If a split system is a logical choice for your application, then the
> savings you are seeing may be realistic. If you want to deterime
the
> "maximum possible" savings in your , I think you should
consider a
> cooling system which modulates the cooling (no compressor cycling
on and
> off). That should control humidity much better.
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "aymericnovel"
> <aymericnovel@> wrote:
> >
> > Hi,
> > I have simulated a 90m² apartment in HoChiMin, vietnam. This is my
> > first study in such a humid climate so I apologize if my question
is
> > trivial. Here is my problem:
> >
> > I use the SingleSpeed DX coil in each cooled zone to simulate a
split
> > system.
> > It recirculates only room air. The temperature setpoint for zone
is
> > 26°C.
> > My study aimed to quantify benefits on cooling energy consumption
of
> > actions on the envelope (use of insulating concrete, low SµHGC
> > windows) and reduction of lighting related internal loads. So far,
> > very logical.
> >
> > And logically, I found that my sensible loads are reduced (about
30%).
> >
> > But, the DXCoil adapts to a lower sensible load by blowing less
air
> > at the same temperature. For an idea here are the 2 configuration
at
> > the air outlet of the coil:
> > High sensible load => 0.08kg/s at about 13.5°C
> > Low sensible load => 0.05kg/s at 13.5°C
> >
> > Logically, in the second case, the sensible cooling rate
delivered is
> > smaller, according to the fact sensible load is indeed smaller.
> > BUT, the latent load increases accordingly. The SHR (Sensible Heat
> > Ratio) decreases in the second case, making the latent part
bigger:
> > High sensible load => SHR = 0.7
> > Low sensible load => SHR = 0.6
> >
> > So, when looking at the result on the total cooling rate, it is
not
> > as fruitful as expected...I guess it is a known fact for engineers
> > who are used to work with high outdoor humidity ratio
> >
> > Is it because the coil is "single speed" that the regulation is
> > automatically made by airflowrate? Is there a way to modify the
blown
> > air temperature instead? Indeed, that would create energy savings
> > also on the latent part to blow the same airflow rate at a higher
> > temperature if sensible load is increased? Isn't that the tendency
> > of current evaporator to increase SHR? Should I change the object
I
> > use? I guess it is all related to "how the object calculates the
> > blown air temperature"...
> >
> > If somebody could help me clear my mind on this topic, I would be
> > grateful!
> >
> > Tnaks a lot,
> > Aymeric
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/