[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Adaptation to sensible load variation of the object Coil:Cooling:DX:singleSpeed
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Adaptation to sensible load variation of the object Coil:Cooling:DX:singleSpeed
- From: "JV Dirkes II" <jvd2pe@xxxxxxx>
- Date: Thu, 12 Feb 2009 12:27:09 -0000
- Delivered-to: linda@xxxxxxxxxx
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1234440694; bh=cJJUtUf5LY6keOU1/PCmCai+J3hLwxOOGi40sRWbHlM=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=OuUZ6h1yfj1wn8+OhHQgQdBp/7RJDlW2yuDYfrH9Jb6qamc7a3iD/EawMLX4QXXkMy4EecLiUA+/u035G5dd1DHw/5lRAr8ldQQ260NY1KT7wqzs3vIY1CcBioilq8FK
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=ARJ3MXSV4UfAjz9fsBhfJrr08ZtHMFowg8H+W45GQt7LMdcXS7zDTwRxtdztsi4EiXC30RkX66ZFZp6vBWkJpr8hYlMYUEIwW9JeJQSY5CVg0T0lLIshOPR79GixKfBb;
- In-reply-to: <gn0i5p+rpds@eGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Dear Aymeric,
I cannot look it up to confirm this, but I think that there are two
variables which affect the discharge air temperature.
One of them is in SET POINT MANAGER:SINGLE ZONE COOLING: the "minimum
supply air temperature" field.
The other is in SYSTEM SIZING: the "Central cooling design supply air
temperature" field.
Sometimes, I set these to different values, then report the node
temperature value and airflow rate to see which one is in use. I recall
that E+ does not use the one I expect, so it's worth checking.
I hope this helps!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "aymericnovel"
<aymericnovel@...> wrote:
>
> Thank you for quickly answering. It is already some considerations I
> will take care of.
> Now, I know the cooling coil is sized by E+ based on sensible load.
> My technical question is more about: Can it be sized by changing the
> blown air temperature instead of the airflow rate? or does the E+
> code leave no choice for that?
> I mean now it keeps blowing air at 13.5°C in the zone but it
reduces
> airflow rate from 0.08kg/s to 0.05kg/s to reduce cooling capacity.
> Could it be more like keeping airflow rate at 0.08kg/s and blowing
> air at 15°C or 16°C?
>
> Regards,
> Aymeric
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II"
> jvd2pe@ wrote:
> >
> > Dear Aymeric,
> >
> > Some general considerations:
> >
> > Split system DX systems always have difficulty controlling
> humidity; the
> > thermostat senses only temperature in most cases. In addition, the
> > cooling coil is not designed or intended for high latent loads
> > (generally a sensible heat ratio of ~0.7 is expected). The fact
> that
> > the compressor cycles on and off compounds the humidity control
> > problems, since no humidity gets removed during an "off" cycle. In
> > fact, moisture on the cooling coil can even get re-absorbed if the
> fan
> > continues to operate while the compressor is off.
> >
> > Your system gets sized by E+ according to sensible load, not latent
> > load. When you reduce the sensible load, but latent loads remain
> > unchanged, the space humidity will rise because the DX coil
> > (correctly) canot handle the higher sensible heat ratio.
> >
> > If a split system is a logical choice for your application, then the
> > savings you are seeing may be realistic. If you want to deterime
> the
> > "maximum possible" savings in your , I think you should
> consider a
> > cooling system which modulates the cooling (no compressor cycling
> on and
> > off). That should control humidity much better.
> >
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "aymericnovel"
> > <aymericnovel@> wrote:
> > >
> > > Hi,
> > > I have simulated a 90m² apartment in HoChiMin, vietnam. This is
my
> > > first study in such a humid climate so I apologize if my question
> is
> > > trivial. Here is my problem:
> > >
> > > I use the SingleSpeed DX coil in each cooled zone to simulate a
> split
> > > system.
> > > It recirculates only room air. The temperature setpoint for zone
> is
> > > 26°C.
> > > My study aimed to quantify benefits on cooling energy consumption
> of
> > > actions on the envelope (use of insulating concrete, low SµHGC
> > > windows) and reduction of lighting related internal loads. So far,
> > > very logical.
> > >
> > > And logically, I found that my sensible loads are reduced (about
> 30%).
> > >
> > > But, the DXCoil adapts to a lower sensible load by blowing less
> air
> > > at the same temperature. For an idea here are the 2 configuration
> at
> > > the air outlet of the coil:
> > > High sensible load => 0.08kg/s at about 13.5°C
> > > Low sensible load => 0.05kg/s at 13.5°C
> > >
> > > Logically, in the second case, the sensible cooling rate
> delivered is
> > > smaller, according to the fact sensible load is indeed smaller.
> > > BUT, the latent load increases accordingly. The SHR (Sensible Heat
> > > Ratio) decreases in the second case, making the latent part
> bigger:
> > > High sensible load => SHR = 0.7
> > > Low sensible load => SHR = 0.6
> > >
> > > So, when looking at the result on the total cooling rate, it is
> not
> > > as fruitful as expected...I guess it is a known fact for engineers
> > > who are used to work with high outdoor humidity ratio
> > >
> > > Is it because the coil is "single speed" that the regulation is
> > > automatically made by airflowrate? Is there a way to modify the
> blown
> > > air temperature instead? Indeed, that would create energy savings
> > > also on the latent part to blow the same airflow rate at a higher
> > > temperature if sensible load is increased? Isn't that the tendency
> > > of current evaporator to increase SHR? Should I change the object
> I
> > > use? I guess it is all related to "how the object calculates the
> > > blown air temperature"...
> > >
> > > If somebody could help me clear my mind on this topic, I would be
> > > grateful!
> > >
> > > Tnaks a lot,
> > > Aymeric
> > >
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/