Couple of questions because I am running into some issues. The first
is can all this be done with the HVAC templates and if so which ones?

The way I have started is to set up a HVACTemplate:Zone:VAV and
System:VAV and set all the minimum and maximums the same and have no
turndown on the VAV. This was my understanding on how to get a CAV
system from the template. Is this right? should i be using
AirTerminal:SingleDuct:ConstantVolume:Reheat or Uncontrolled instead?

Then I am going into the expanded idf and trying to add a
ZoneHVAC:FourPipeFanCoil manually, but there are object parameters for
outdoor air which i don't have because it is just recirculating the
zone air. Also it seems like the outlet from the VAV/CAV is the same
node as the outlet for the fan coil, which is the zone inlet. I
thought zones could have only one air inlet and outlet

Can you see where I am going with this. Looking for a little more
direction.

I do appreciate the help

-
aj

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> You can have both. Start with a 1 zone model first. Autosizing the 
> equipment will size each to meet the total zone load, so after the
first 
> run, manually size the systems as appropriate for your application.
> 
> Alan Jackson wrote:
> >
> > Sorry to bring this up again but did not get any response the initial
> > go around. I would like to model a CV air system supplying ventilation
> > and cooling to a zone that also has perimeter recirculation console
> > FCUs. Do I need to have a seperate perimeter zone just for the FCUs or
> > can I have both CV and FCU in the same zone using direct air or
> > something like that.
> >
> > I just don't want to go back and have to add perimeter zones after
> > finding out it doesn't work, otherwise i would just attempt it myself.
> >
> > thanks in advance
> >
> > -
> > aj
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/