The air terminal units (TU) have both an air inlet and air outlet node.
For this specific object, an "internal" (i.e., used internally in the
software) damper node is also used. In this case these are:
TU Air Inlet Node = SPACE1-1 ATU In Node
TU Damper Inlet = SPACE1-1 Zone Coil Air In Node
TU Air Outlet = SPACE1-1 In Node
These nodes are used to specify the connection scheme for the objects
used in a simulation. The TU's are connected to the zones. Splitters are
used to connect an air loop to multiple zones. The splitter is connected
to the terminal unit (AirLoopHVAC:ZoneSplitter Outlet 1 Node Name
connected to AirTerminal:SingleDuct:VAV:Reheat Air Inlet Node) and the
terminal unit is connected to the zone (
AirTerminal:SingleDuct:VAV:Reheat Air Outlet Node connected to Zone 1
Air Inlet Node). The AirTerminal:SingleDuct:VAV:Reheat Damper Node is
used to configure the reheat coil (Damper Outlet Node is equal to the
reheat coil inlet node and the reheat coil outlet node is equal to the
AirTerminal:SingleDuct:VAV:Reheat Outlet Air Node). All the objects
shown below are connected together and are simulated in a series fashion
to pass information from one object to the next. The
ZoneHVAC:AirDistributionUnit object is also used to specify which type
of terminal unit is used in the simulation. You can search for node
names (or any string) in a text editor to see how these connections are
made. HVAC-Diagram also uses the node names to draw the object
connections so you can see how things are configured.
Coil:Heating:Water,
SPACE1-1 Zone Coil, !- Name
ReheatCoilAvailSched, !- Availability Schedule Name
autosize, !- U-Factor Times Area Value {W/K}
autosize, !- Maximum Water Flow Rate {m3/s}
SPACE1-1 Zone Coil Water In Node, !- Water Inlet Node Name
SPACE1-1 Zone Coil Water Out Node, !- Water Outlet Node Name
SPACE1-1 Zone Coil Air In Node, !- Air Inlet Node Name
SPACE1-1 In Node, !- Air Outlet Node Name
UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
autosize, !- Nominal Capacity {W}
82.2, !- Design Inlet Water Temperature {C}
16.6, !- Design Inlet Air Temperature {C}
71.1, !- Design Outlet Water Temperature {C}
32.2; !- Design Outlet Air Temperature {C}
AirLoopHVAC:ZoneSplitter,
Zone Supply Air Splitter 1, !- Name
Zone Eq In Node, !- Inlet Node Name
SPACE1-1 ATU In Node, !- Outlet 1 Node Name
SPACE2-1 ATU In Node, !- Outlet 2 Node Name
SPACE3-1 ATU In Node, !- Outlet 3 Node Name
SPACE4-1 ATU In Node, !- Outlet 4 Node Name
SPACE5-1 ATU In Node; !- Outlet 5 Node Name
ZoneHVAC:EquipmentConnections,
SPACE1-1, !- Zone Name
SPACE1-1 Eq, !- Zone Conditioning Equipment List Name
SPACE1-1 In Node, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
SPACE1-1 Node, !- Zone Air Node Name
SPACE1-1 Out Node; !- Zone Return Air Node Name
AirTerminal:SingleDuct:VAV:Reheat,
SPACE1-1 VAV Reheat, !- Name
ReheatCoilAvailSched, !- Availability Schedule Name
SPACE1-1 Zone Coil Air In Node, !- Damper Air Outlet Node Name
SPACE1-1 ATU In Node, !- Air Inlet Node Name
autosize, !- Maximum Air Flow Rate {m3/s}
Constant, !- Zone Minimum Air Flow Input Method
0.3, !- Constant Minimum Air Flow Fraction
, !- Minimum Air Flow Fraction Schedule Name
SPACE1-1 Zone Coil Water In Node, !- Hot Water or Steam Inlet Node Name
Coil:Heating:Water, !- Reheat Coil Object Type
SPACE1-1 Zone Coil, !- Reheat Coil Name
autosize, !- Maximum Hot Water or Steam Flow Rate {m3/s}
0.0, !- Minimum Hot Water or Steam Flow Rate {m3/s}
SPACE1-1 In Node, !- Air Outlet Node Name
0.001, !- Convergence Tolerance
NORMAL; !- Damper Heating Action
ZoneHVAC:AirDistributionUnit,
SPACE1-1 ATU, !- Name
SPACE1-1 In Node, !- Air Distribution Unit Outlet Node Name
AirTerminal:SingleDuct:VAV:Reheat, !- Air Terminal Object Type
SPACE1-1 VAV Reheat; !- Air Terminal Name
yangchen19851226 wrote:
>
> AirTerminal:SingleDuct:VAV:Reheat,
> SPACE1-1 VAV Reheat, !- Name
> FanAvailSched, !- Availability Schedule Name
> SPACE1-1 Zone Coil Air In Node, !- Damper Air Outlet Node Name
> SPACE1-1 ATU In Node, !- Air Inlet Node Name
> autosize, !- Maximum Air Flow Rate {m3/s}
> 0.3, !- Zone Minimum Air Flow Fraction
> SPACE1-1 Zone Coil Water In Node, !- Sensor Node Name
> Coil:Heating:Water, !- Reheat Coil Object Type
> SPACE1-1 Zone Coil, !- Reheat Coil Name
> autosize, !- Maximum Reheat Water Flow Rate {m3/s}
> 0.0, !- Minimum Reheat Water Flow Rate {m3/s}
> SPACE1-1 In Node, !- Air Outlet Node Name
> 0.001, !- Convergence Tolerance
> Reverse; !- Damper Heating Action
>
> Can you tell me what is the difference between SPACE1-1 Zone Coil Air
> In Node and SPACE1-1 In Node?
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/