Re: [EnergyPlus_Support] 100% fresh air with local heating and cooling
See documentation for Controller:MechanicalVentilation (V3.0).
andystone101 wrote:
>
> Hi,
>
> I'm trying to model a building which has an air handling unit with
> heat recovery supplying 100% fresh air to a number of rooms at roughly
> room temperature and has local heating and cooling systems in each
> room. Is there an example somewhere showing how to set this up?
>
> The problem that I am having is getting the AHU to supply 100% fresh
> air with the flow rate varying according to the occupancy of the space
> (my outdoor air demand is related to space occupancy). Things I've tried:
> - Using the economiser to force 100% fresh air, but that seems to
> disable the heat recovery system.
> - Fixing the minimum outside air rate to be the same as the system
> flow rate, but then the flow rate doesn't change with occupancy.
> - I've managed to get the right fresh air rate but with recirculated
> air included (basically the default behaviour).
>
> Do I need to manually add up all of the zones' fresh air demand and
> create a schedule for that? I was hoping to get the sizing routines to
> do the work for me - any pointers?
>
> Thanks in advance,
>
> Andy
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/