When I plot the COP vs PLR dependence taken from the file 'Chillers.idf' for specific chillers (please see the file
COP vs PLR (EnergyPlus).jpg ) it shows that for some chillers at e.g. PLR=0.4 the COP is 4times higher than for PLR=1, and for PLR =0.5 most of the chillers have 2times higher COP than at PLR=1.
For me it's unrealistic, especially when i compare these results to the catalogue data given from the producers (where the COP/COP_ref value reaches its maximum usually for PLR=0.5 and is about 1.6)
Do I do a mistake somewhere? COP/COP_ref = 1/ChillerEIRFPLR, right?
Or maybe this problem is related to my next question: COP vs PLR performance in catalogue data is mostly rated under ARI conditions, for instance for water2water chillers and PLR=1 ECWT=29.4C and for PLR=0.5 ECWT=18.3C. Do the ChillerEIRPLR curves are rated for constant ECWT? If yes how can I modify PLR curves rated according to ARI standard into curves for constant ECWT?