See below. d_h51@xxxxxxxxx wrote: Hi all,Actually this is wrong, due to a confusing feature of EIRFPLR: EIRFPLR contains a PLR factor within it. The correct formula is COP/COP_ref = PLR/ChillerEIRFPLR. This also holds true for Doe-2, eQuest etc. Here's the derivation: COP = CoolOut/EnergyIn PLR = CoolOut/AvailCap EnergyIn = (AvailCap/COP_nom)*EIRFPLR*EIRFT (this is from the EPlus code. Note the use of AvailCap on the right hand side of the equation, rather than what you'd expect: CoolOut =AvailCap*PLR) So COP = (PLR*AvailCap) / ( (AvailCap/Cop_npm)*EIRFPLR*EIRFT) and COP/COP_nom = PLR/(EIRFPLT*EIRFT) Fred Buhl
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.