Re: [EnergyPlus_Support] Coil:Cooling:DX:SingleSpeed - Flow Rate to Rated Total Capacity



The DX Coil model assumes the air flow per rated cooling capacity is 
within a certain range. Manufacturers typically operate within this 
range. Look at the air flow rate and capacity for the DX coil. Make sure 
the air flow per capacity is within the range of 0.00002684 - 0.00006713 
(m3/W). Or 200 cfm/ton - 500 cfm/ton.

AirFlowPerCapacityRatio (m3/W) = Rated Air Flow Rate (m3) / Rated Total 
Cooling Capacity (W)
 
I typically choose to operate between 0.00004 - 0.00005 m3/W. Approx 300 
- 400 cfm/ton.

khaysepro wrote:
>
>
> I am trying to model an existing system to verify energy usage for a 
> LEED project. I am getting a severe error when I run the model because 
> the cooling capacity is sized for a design peak load condition that 
> does not exist in actual usage. Design airflow and cooling capacity 
> was calculated by a commercial load estimating software package that 
> apparently does not model DX coils a rigorously as E+. Is there away a 
> to work around the airflow per cooling capacity limits for this type 
> of coil?
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/