Fan coil unit: the fan is always on when the unit is scheduled on.
Unit Ventilator: on when scheduled on AND there is a load.
So it looks like the Unit Ventilator does what you want.
Fred Buhl
andystone101 wrote:
> Hi,
>
> I've seen mentioned on this newsgroup that the fancoil object only switches on and off depending on the availability schedule, but the top of page 872 of the engineering reference suggests that it also switches off when there is no (or low) heating/cooling load. Which one of these is correct? From what I can tell the fan of the fancoil always runs if it is scheduled to be available even if there is no load on the unit.
>
> I'm looking for something that only switches on the fan when there is a cooling demand (I'm simulating a local cooling system with no fresh air supplied). Does the unit ventilator do this?
>
> Thanks,
>
> Andy
>
>
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/