Re: [EnergyPlus_Support] Hybrid Ventilation Control



Maybe you could try running each month (or group of months) with each 
month's simulation having it's own maximum outdoor dry-bulb temp. Then 
append the data from each csv.

Sherif Ezzeldin wrote:
>
>
> Lixing,
>  
> Thank you for your prompt reply
>  
> The alternative way works with only one annual CSP but, in my case, I 
> have several Monthly CSP. Therefore, I have to select one of those CSP 
> values which is not ideal.
>  
> Concerning the wish list, in order to solve the problem ideally, I 
> could suggest that:
> 1) The hybrid ventilation control may need to have the opportunity of 
> adding a schedule for the maximum and the minimum outdoor temperatures 
> instead of just values.
> 2) The hybrid control mode 4 (ventilation rate) could firstly compare 
> the calculated ventilation rate from the airflow network model with 
> the minimum value (as it does), secondly, compare the zone temperature 
> with the CSP, and then predict the hybrid status.
> 3) As well, one of my colleagues suggested that the "System 
> Availability Manager: High Temperature Turn On" could be used as an 
> alternative only if an "availability schedule name" is added to it as 
> in "System Availability Manager: Low Temperature Turn Off"
>  
> I don't know how difficult / important these suggestions could be but 
> I hope IAQ will be considered soon 
>  
> Kind regards,
> Sherif
>
>  
>
> ------------------------------------------------------------------------
> *From:* Lixing Gu <gu@xxxxxxxxxxxx>
> *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> *Sent:* Friday, May 8, 2009 2:12:34 PM
> *Subject:* Re: [EnergyPlus_Support] Hybrid Ventilation Control
>
> Sherif:
>  
> The hybrid ventilation control is mainly used to save energy and 
> prevent simultaneous natural ventilation and HVAC operation. The 
> IAQ control was not considered when the object was developed. We need 
> to reconsider a possible combination to let user make IAQ control. I 
> will write this one into a wish list. Do you have more suggestions?
>  
> The alternative way you mentioned is to make scheduled maximum and 
> minimum outdoor temperature, such as scheduled CSP. Does this meet 
> your needs for the time being? 
>  
> Lixing
>  
>
>     ----- Original Message -----
>     *From:* Sherif Ezzeldin <mailto:shezzeldin@xxxxxxxxx>
>     *To:* EnergyPlus_Support@ yahoogroups. com
>     <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>
>     *Sent:* Friday, May 08, 2009 6:39 AM
>     *Subject:* Re: [EnergyPlus_ Support] Hybrid Ventilation Control
>
>     Hi,
>      
>     Thank you Lixing, Richard, Linda and Fabio for your concern and
>     support
>      
>     I've looked through the detailed report variables as recommended
>     It was very helpful to understand more the performance of the
>     system and the control logic
>      
>     Through different timesteps in an hour, the hybrid status is
>     alternating from 1 (allowing natural ventilation) to 2 (mechanical
>     ventilation) according to the cooling setpoint temperature (CSP)
>     and the cooling demand. Once the air temperature reached the CSP
>     (27C), the mechanical cooling system is operating in order to keep
>     the air temperature just below the CSP while the supplied fresh
>     air exceeds the minimum requirements (no problem).
>      
>     My problem summarizes in that, after several timesteps of HVAC
>     operation, the hybrid status changes to 1 as the outdoor
>     temperature (30C) is between the min.& max. values (15-35C) while
>     natural ventilation is not permitted as the outdoor temperature is
>     higher than the indoor temperature (27C).  At these moments, the
>     airflow is below the minimum ventilation rate. Accordingly,
>     the hourly supplied amount of fresh air (by both HVAC and Natural
>     Ventilation) doesn't match the minimum requirements which affect
>     the Indoor Air Quality.
>      
>     Since the ventilation rate due to natural ventilation is below the
>     minimum requirements at the critical moments, the system should
>     then switch to mechanical ventilation with minimum ventilation
>     rate to maintain acceptable Indoor Air Quality. Therefore, a
>     combined control mode will be helpful at these circumstances, am I
>     right?
>      
>     Another alternative could solve the problem by matching the
>     maximum outdoor temperature with the CSP but we can only specify
>     just one max. outdoor temp. for the whole year. In that case,
>     Which value could be used when we use different seasonal/monthly
>     CSP (which is my situtation as well)?
>      
>     I appreciate very much your help
>      
>     Kind regards,
>     Sherif
>
>      
>     ------------------------------------------------------------------------
>     *From:* Lixing Gu <gu@xxxxxxxx. edu>
>     *To:* EnergyPlus_Support@ yahoogroups. com
>     *Sent:* Wednesday, May 6, 2009 8:47:23 PM
>     *Subject:* Re: [EnergyPlus_ Support] Hybrid Ventilation Control
>
>     Sherif:
>      
>     I think Rich answers your question regarding the hybrid status
>     value between 1 and 2. I am trying to clarify the control logic.
>     When the control mode is temperature, the control will check
>     whether the outdoor temperature is between min and max temperature
>     specified in the inputs, such as 15 and 35C you mentioned. If it
>     OK, the control also check whether HVAC system is required to turn
>     on or not, by checking indoor temperature. For example, if the
>     indoor temperature in the controlled zone is above the cooling
>     setpoint. HVAC system turns on.  
>      
>     The control mode 4 is only working with the AirflowNetwork model.
>     If the infiltration by opening windows is above the scheduled
>     input. HVAC system turns off and windows are open, regardless of
>     other conditions.
>      
>     Hope this helps.
>      
>     Lixing
>
>         ----- Original Message -----
>         *From:* Sherif Ezzeldin <mailto:shezzeldin@xxxxxxxxx>
>         *To:* EnergyPlus_Support@ yahoogroups. com
>         <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>
>         *Sent:* Wednesday, May 06, 2009 11:40 AM
>         *Subject:* Re: [EnergyPlus_ Support] Hybrid Ventilation Control
>
>         Lixing,
>          
>         Thanks for your concern
>          
>         The main concern is designing an acceptable indoor environment
>         is to maintain both Thermal Comfort and Indoor Air Quality
>         requirements.
>          
>         Concerning Indoor Air Quality requirements, a minimum
>         ventilation rate (10l/s/person= 1.29ACH) is required to
>         maintain acceptable level of CO2 in an office space. A
>         successful hybrid design should provide that ventilation rate
>         by natural ventilation and switch to mechanical ventilation
>         just when the minimum value couldn't be met.
>          
>         At the same time, the zone operative temperature should lie
>         within the upper & lower thermal comfort boundaries. A
>         successful hybrid design should maintain natural ventilation
>         as long as the  zone operative temperature is within the
>         comfort boundaries, once it reaches the upper comfort boundary
>         temperature (cooling setpoint temperature CSP), the system
>         should switch to mechanical cooling  
>         In EnergyPlus, if I set the control mode to 1 (temperature)
>         and the min. and max. outdoor temp. to 15C and 35C as in the
>         example file, when the outdoor temp. reaches 32C and the
>         indoor temp is 28C and the CSP is 26C , in that case the
>         mechanical system should operate and the hybrid status should
>         be equal to 2 but the hybrid status value is between 1 and 2.
>         My explanation could be that since the outside lies between
>         15C and 35C, then hybrid control allows natural ventilation,
>         and since the outdoor temp is higher than the indoor temp,
>         then natural ventilation is not allowed.
>          
>         Alternatively, if I set the control mode to 4 (Ventilation
>         rate), the system just compare the predicted ventilation rate
>         with the minimum value regardless to the cooling setpoint,
>         therefore, during summer, the indoor temperature exceeds the
>         upper comfort boundary temperature but with acceptable
>         ventilation rate.
>          
>         Could you please help me may be there is something I
>         miss-understood?
>          
>         Kind regards,
>         Sherif
>
>         ------------------------------------------------------------------------
>         *From:* Lixing Gu <gu@xxxxxxxx. edu>
>         *To:* EnergyPlus_Support@ yahoogroups. com
>         *Sent:* Wednesday, May 6, 2009 2:24:48 PM
>         *Subject:* Re: [EnergyPlus_ Support] Hybrid Ventilation Control
>
>         Sherif:
>          
>         The existing EnergyPlus only allows one of controls at the
>         same time. Any combination is not allowed. Could you provide
>         your control in detail, so that possible enhancement will be
>         considered?
>          
>         Thanks.
>          
>         Lixing
>
>             ----- Original Message -----
>             *From:* Sherif Ezzeldin <mailto:shezzeldin@xxxxxxxxx>
>             *To:* EnergyPlus_Support@ yahoogroups. com
>             <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>
>             *Sent:* Wednesday, May 06, 2009 6:26 AM
>             *Subject:* [EnergyPlus_ Support] Hybrid Ventilation Control
>
>             Hi,
>
>              
>
>             I'm trying to improve the performance of a hybrid
>             ventilation scheme in an office space
>
>              
>
>             I'm using EnergyPlus version 2.2
>
>              
>
>             Concerning the control mode in the "Hybrid Ventilation
>             control" model, we have to specify either to control
>             natural and mechanical ventilation by temperature (control
>             mode=1) or by ventilation rate (control mode=4)
>
>              
>
>             Is there a way to combine these two control modes together
>             and to let the program first to calculate the
>             temperature (compare it with the acceptable temperature
>             ranges) and the ventilation rate (compare it with the
>             minimum ventilation rate) all together and then decide
>             whether to provide natural or mechanical ventilation?
>
>              
>
>             Thanks for your support
>
>              
>
>             Kind regards,
>
>             Sherif
>
>              
>
>
>
>
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/