RE: [EnergyPlus_Support] Regarding the evaporative cooler + Chiller
Use one of the evap coolers that controls to a leaving setpoint temperature, the so-called ResearchSpecial models. These will stop conditioning if the entering conditions already meet setpoint. Then use outside air reset setpoint manager to adjust a temperature setpoint on the cooler's outlet node.
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of vignesh kumar
Sent: Sat 5/9/2009 6:45 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Regarding the evaporative cooler + Chiller
Hi guys
im actually working on a building model with both the chiller and
evaporative pre cooler in Ahu system , what i want to do is i want the
evaporative pre cooler to run when the temperature of the outsider air is
between say15 - 20 degree celcius and during that time the chiller should
not operate and if the temperature of the outside air becomes more than 20
the chiller should operate and the evaporative pre cooler should stop , i
have figured out how to stop the chiller working below 20 degree celcius but
im having problem to configure the evaporative pre cooler to work between
these temperature , if any one knows how to configure this please let me
know
Thanks and Regards
--
vigneshkumar
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
Attachment not found:
d:\eudora\attach\winmail13.dat