Re: [EnergyPlus_Support] AFN linkage setup on zone ERV loop




Xia:

When ERV and the AirflowNetwork model are used together, the exhaust air outlet node defined in�an heat exchanger�is assumed to be outside node. Please look at an example file how to connect nodes: AirflowNetwork_Multizone_SmallOfiice_HeatRecoveryHXSL.idf.

Lixing
> ----- Original Message -----
From: <mailto:fang_xia@xxxxxxxxx>xia fang
To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, May 12, 2009 1:03 PM
Subject: [EnergyPlus_Support] AFN linkage setup on zone ERV loop
> 	> 
> 
> Hi, I have a question on how to properly simulate zone ERV loop in Airflow network.
> �
> The linkage requires to have zone ERV loop nodes into the AFN. But I got stuck when it comes to ERV exhaust outlet node “node 1” connection to which “node 2”. In order to bypass the
> Error messages, I connected the ERV exhaust outlet node to ERV outside air inlet node. But this really does not sound right. Unless I put the heat recovery into the outside air system which
> Can be connected to the main air handling unit. Is this the right way to simulate AFN zone ERV loop? I do have a single zone�.
> �
> Thanks ahead for your response.
> �
> Xia



__._,_.___

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.� Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=13522/stime=1242149040>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmZ3Qwa2tlBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEyNDIxNDkwNDA->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkcTRwbmVoBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMjQyMTQ5MDQw>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___