[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: how to size component and plant



Hi,
  I have sent the idf file to you.Please check it.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Send me your file:
> 
> rraustad@...
> 
> yangchen19851226 wrote:
> >
> >
> > Yeah,system and plant objects were both set in the idf file,but the 
> > equipment sizes were not reported in the eio file.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad 
> > <RRaustad@> wrote:
> > >
> > > Are you saying you:
> > >
> > > 1) autosized all your equipment (as shown in the previous email)
> > > 2) included zone and system sizing objects
> > > 3) turned on sizing in the simulation control object
> > >
> > > and the equipment sizes ARE NOT reported in the eio file?
> > >
> > > yangchen19851226 wrote:
> > > >
> > > >
> > > > Hi,
> > > > Thank you for your reply.My problem is I can only get data of zone
> > > > sizing,the datas of equipment and plant can be displayed in csv
> > > > file.Can you tell me the reason?
> > > >
> > > > regards
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > <RRaustad@> wrote:
> > > > >
> > > > > Equipment is autosized by specifying the word "autosize" for 
> > specific
> > > > > inputs in various equipment objects. See example file 
> > 5ZoneWaterSystems.
> > > > >
> > > > > For example, in 5ZoneWaterSystems.idf the maximum flow rate in 
> > the hot
> > > > > water plant can be autosized. The use of autosizing requires sizing
> > > > > objects to specify design intent.
> > > > >
> > > > > PlantLoop,
> > > > > Hot Water Loop, !- Name
> > > > > Water, !- Fluid Type
> > > > > Hot Loop Operation, !- Plant Equipment Operation Scheme Name
> > > > > HW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
> > > > > 100, !- Maximum Loop Temperature {C}
> > > > > 10, !- Minimum Loop Temperature {C}
> > > > > autosize, !- Maximum Loop Flow Rate {m3/s}
> > > > >
> > > > > Sizing:Plant,
> > > > > SHWSys1, !- Plant or Condenser Loop Name
> > > > > HEATING, !- Loop Type
> > > > > 56, !- Design Loop Exit Temperature {C}
> > > > > 5.0; !- Loop Design Temperature Difference {deltaC}
> > > > >
> > > > > Equipment connected to the plant can also be autosized in a similar
> > > > > manner and require zone and system sizing objects. It is usually 
> > better
> > > > > to autosize all equipment in a simulation instead of manually sizing
> > > > > some equipment and autosizing other equipment.
> > > > >
> > > > > AirLoopHVAC,
> > > > > VAV Sys 1, !- Name
> > > > > VAV Sys 1 Controllers, !- Controller List Name
> > > > > VAV Sys 1 Avail List, !- Availability Manager List Name
> > > > > autosize, !- Design Supply Air Flow Rate {m3/s}
> > > > >
> > > > > Coil:Heating:Water,
> > > > > SPACE1-1 Zone Coil, !- Name
> > > > > ReheatCoilAvailSched, !- Availability Schedule Name
> > > > > autosize, !- U-Factor Times Area Value {W/K}
> > > > > autosize, !- Maximum Water Flow Rate {m3/s}
> > > > > SPACE1-1 Zone Coil Water In Node, !- Water Inlet Node Name
> > > > > SPACE1-1 Zone Coil Water Out Node, !- Water Outlet Node Name
> > > > > SPACE1-1 Zone Coil Air In Node, !- Air Inlet Node Name
> > > > > SPACE1-1 In Node, !- Air Outlet Node Name
> > > > > UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
> > > > > autosize, !- Nominal Capacity {W}
> > > > >
> > > > > AirTerminal:SingleDuct:VAV:Reheat,
> > > > > SPACE1-1 VAV Reheat, !- Name
> > > > > ReheatCoilAvailSched, !- Availability Schedule Name
> > > > > SPACE1-1 Zone Coil Air In Node, !- Damper Air Outlet Node Name
> > > > > SPACE1-1 ATU In Node, !- Air Inlet Node Name
> > > > > autosize, !- Maximum Air Flow Rate {m3/s}
> > > > > Constant, !- Zone Minimum Air Flow Input Method
> > > > > 0.3, !- Constant Minimum Air Flow Fraction
> > > > > , !- Minimum Air Flow Fraction Schedule Name
> > > > > SPACE1-1 Zone Coil Water In Node, !- Hot Water or Steam Inlet 
> > Node Name
> > > > > Coil:Heating:Water, !- Reheat Coil Object Type
> > > > > SPACE1-1 Zone Coil, !- Reheat Coil Name
> > > > > autosize, !- Maximum Hot Water or Pump:VariableSpeed,
> > > > > HW Circ Pump, !- Name
> > > > > HW Supply Inlet Node, !- Inlet Node Name
> > > > > HW Pump Outlet Node, !- Outlet Node Name
> > > > > autosize, !- Rated Flow Rate {m3/s}
> > > > > 179352, !- Rated Pump Head {Pa}
> > > > > autosize, !- Rated Power Consumption {W}
> > > > >
> > > > > Sizing:System,
> > > > > VAV Sys 1, !- AirLoop Name
> > > > > sensible, !- Type of Load to Size On
> > > > > autosize, !- Design Outdoor Air Flow Rate {m3/s}
> > > > > 0.3, !- Minimum System Air Flow Ratio
> > > > > 7.0, !- Preheat Design Temperature {C}
> > > > > .008, !- Preheat Design Humidity Ratio
> > > > > {kg-H2O/kg-Air}
> > > > > 11.0, !- Precool Design Temperature {C}
> > > > > .008, !- Precool Design Humidity Ratio
> > > > > {kg-H2O/kg-Air}
> > > > > 12.8, !- Central Cooling Design Supply Air
> > > > > Temperature {C}
> > > > > 16.7, !- Central Heating Design Supply Air
> > > > > Temperature {C}
> > > > > noncoincident, !- Sizing Option
> > > > > no, !- 100% Outdoor Air in Cooling
> > > > > no, !- 100% Outdoor Air in Heating
> > > > > 0.008, !- Central Cooling Design Supply Air
> > > > > Humidity Ratio {kg-H2O/kg-Air}
> > > > > 0.008, !- Central Heating Design Supply Air
> > > > > Humidity Ratio {kg-H2O/kg-Air}
> > > > > DesignDay, !- Cooling Design Air Flow Method
> > > > > 0, !- Cooling Design Air Flow Rate {m3/s}
> > > > > DesignDay, !- Heating Design Air Flow Method
> > > > > 0; !- Heating Design Air Flow Rate {m3/s}
> > > > >
> > > > > Sizing:Zone,
> > > > > SPACE5-1, !- Zone Name
> > > > > 14., !- Zone Cooling Design Supply Air
> > > > > Temperature {C}
> > > > > 50., !- Zone Heating Design Supply Air
> > > > > Temperature {C}
> > > > > 0.009, !- Zone Cooling Design Supply Air Humidity
> > > > > Ratio {kg-H2O/kg-air}
> > > > > 0.004, !- Zone Heating Design Supply Air Humidity
> > > > > Ratio {kg-H2O/kg-air}
> > > > > flow/person, !- Outdoor Air Method
> > > > > 0.00944, !- Outdoor Air Flow per Person {m3/s}
> > > > > 0.0, !- Outdoor Air Flow per Zone Floor Area
> > > > > {m3/s-m2}
> > > > > 0.0, !- Outdoor Air Flow per Zone {m3/s}
> > > > > 0.0, !- Zone Sizing Factor
> > > > > DesignDay, !- Cooling Design Air Flow Method
> > > > > 0, !- Cooling Design Air Flow Rate {m3/s}
> > > > > , !- Cooling Minimum Air Flow per Zone Floor
> > > > > Area {m3/s-m2}
> > > > > , !- Cooling Minimum Air Flow {m3/s}
> > > > > , !- Cooling Minimum Air Flow Fraction
> > > > > DesignDay, !- Heating Design Air Flow Method
> > > > > 0, !- Heating Design Air Flow Rate {m3/s}
> > > > > , !- Heating Maximum Air Flow per Zone Floor
> > > > > Area {m3/s-m2}
> > > > > , !- Heating Maximum Air Flow {m3/s}
> > > > > ; !- Heating Maximum Air Flow Fraction
> > > > >
> > > > > The Simulation Control object must also be configured to run the 
> > sizing
> > > > > procedures.
> > > > >
> > > > > SimulationControl,
> > > > > Yes, !- Do Zone Sizing Calculation
> > > > > Yes, !- Do System Sizing Calculation
> > > > > Yes, !- Do Plant Sizing Calculation
> > > > > Yes, !- Run Simulation for Sizing Periods
> > > > > No; !- Run Simulation for Weather File Run Periods
> > > > >
> > > > >
> > > > > yangchen19851226 wrote:
> > > > > >
> > > > > >
> > > > > > Hi,all
> > > > > > In my simulation,I only get some datas fo zone,such as Des 
> > Sens Cool
> > > > > > Cap Des Heat Mass Flow [kg/s] of zone and system,how can i use 
> > these
> > > > > > datas to autosize component and plant?
> > > > > >
> > > > > > regards
> > > > > >
> > > > > >
> > > > >
> > > > > --
> > > > > Richard A. Raustad
> > > > > Senior Research Engineer
> > > > > Florida Solar Energy Center
> > > > > University of Central Florida
> > > > > 1679 Clearlake Road
> > > > > Cocoa, FL 32922-5703
> > > > > Phone: (321) 638-1454
> > > > > Fax: (321) 638-1439 or 1010
> > > > > Visit our web site at: http://www.fsec.ucf.edu 
> > <http://www.fsec.ucf.edu> <http://www.fsec.ucf.edu 
> > <http://www.fsec.ucf.edu>>
> > > > >
> > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/