Re: [EnergyPlus_Support] AbsorbitionChiller



Prior to V3.0, the absorption chiller does not use an actual loop, the 
model assumes steam and the amount of steam used is available through 
report variables Chiller Steam Consumption Rate and Chiller Steam 
Consumption. For V3.0 and later, a hot water or steam loop MAY be used 
to regenerate the absorption cycle but the use of an actual loop is 
optional. Note that the example file (V3.0 and later shown here) leaves 
the generator node names blank which means a steam loop is assumed. If 
you are using a version prior to V3.0, you must upgrade to the latest 
version in order to connect a steam or hot water loop to the absorption 
chiller. See the Input Output and Engineering Reference for more details.

  Chiller:Absorption,
<snip>
    ,                        !- Generator Inlet Node Name
    ,                        !- Generator Outlet Node Name
    VARIABLEFLOW;            !- Chiller Flow Mode



In order to better serve you, a helpdesk system has been set up for 
managing EnergyPlus user support requests. The helpdesk system includes 
a download area, a knowledge base and troubleshooting area.

To submit new support requests (tickets) or search the knowledge base, 
please go to http://energyplus.helpserve.com 
<http://energyplus.helpserve.com>

You may also submit new tickets and reply to tickets via e-mail at 
EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com> This 
address has been linked to the helpdesk since early May 2008.

EnergyPlus_Support@xxxxxxxxxxxxxxx 
<mailto:EnergyPlus_Support%40yahoogroups.com> will now be primarily a 
user-to-user forum, with occasional input from the EnergyPlus 
development team.

Your message may also be forwarded to the helpdesk system, in which case 
you will receive a separate login for that system.

** If you have an unresolved issue which was posted to the yahoo group, 
please resubmit your request to EnergyPlus-Support@xxxxxxxx 
<mailto:EnergyPlus-Support%40gard.com> Please include any replies to 
date and attach input files as needed.

giovanni.matarrese wrote:
>
>
> Hi,
> I want to integrate my plant with a microCHP with an absorbition 
> chiller to make air conditioning in summer.
> I looked at the example file"AbsorbitionChiller", but I don't 
> understand were the chiller takes heat for its functioning, in fanct 
> the chiller is only linked to the condenser loop and not to the 
> heating loop.
> how can I link the thermal power producted by the microchp to the 
> absorbition chiller?
> thank you.
>
> Giovanni
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/