[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: AbsorbitionChiller
thank you for your answer,
it's true, I'm using the V2.2 for my simulation because, as I told in a previous post and in a submitted ticket to the helpdesk support, the same file that works well in V2.2, exported in V3 and later doesn't work as in the V2.2 and it gives bad results!
I noted that the absorbition chiller in V3 has generator inlet and outlet nodes fields, but to use the new version I first need to solve the problem about the microCHP model that in the V3 doesn't work well...
can you help me about it if I send you my file in V2.2?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Prior to V3.0, the absorption chiller does not use an actual loop, the
> model assumes steam and the amount of steam used is available through
> report variables Chiller Steam Consumption Rate and Chiller Steam
> Consumption. For V3.0 and later, a hot water or steam loop MAY be used
> to regenerate the absorption cycle but the use of an actual loop is
> optional. Note that the example file (V3.0 and later shown here) leaves
> the generator node names blank which means a steam loop is assumed. If
> you are using a version prior to V3.0, you must upgrade to the latest
> version in order to connect a steam or hot water loop to the absorption
> chiller. See the Input Output and Engineering Reference for more details.
>
> Chiller:Absorption,
> <snip>
> , !- Generator Inlet Node Name
> , !- Generator Outlet Node Name
> VARIABLEFLOW; !- Chiller Flow Mode
>
>
>
> In order to better serve you, a helpdesk system has been set up for
> managing EnergyPlus user support requests. The helpdesk system includes
> a download area, a knowledge base and troubleshooting area.
>
> To submit new support requests (tickets) or search the knowledge base,
> please go to http://energyplus.helpserve.com
> <http://energyplus.helpserve.com>
>
> You may also submit new tickets and reply to tickets via e-mail at
> EnergyPlus-Support@... <mailto:EnergyPlus-Support%40gard.com> This
> address has been linked to the helpdesk since early May 2008.
>
> EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> will now be primarily a
> user-to-user forum, with occasional input from the EnergyPlus
> development team.
>
> Your message may also be forwarded to the helpdesk system, in which case
> you will receive a separate login for that system.
>
> ** If you have an unresolved issue which was posted to the yahoo group,
> please resubmit your request to EnergyPlus-Support@...
> <mailto:EnergyPlus-Support%40gard.com> Please include any replies to
> date and attach input files as needed.
>
> giovanni.matarrese wrote:
> >
> >
> > Hi,
> > I want to integrate my plant with a microCHP with an absorbition
> > chiller to make air conditioning in summer.
> > I looked at the example file"AbsorbitionChiller", but I don't
> > understand were the chiller takes heat for its functioning, in fanct
> > the chiller is only linked to the condenser loop and not to the
> > heating loop.
> > how can I link the thermal power producted by the microchp to the
> > absorbition chiller?
> > thank you.
> >
> > Giovanni
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/