If you are using the simple baseboard
model (ZoneBaseboard:OutdoorTemperatureControlled), then it acts like internal
gains and is not a thermostatically controlled heating system. This is for those
self-contained, free-standing heating appliances that don’t really control
zone temperature. If you want good control then you have to
use actual HVAC equipment such as ZoneHVAC:Baseboard:Convective:Electric. From:
Thanks. I will try that. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.