Re: [EnergyPlus_Support] Outside air control



Report the outside air node mass (or volume) flow rate to see if it is 
actually 0. In this example "Outside Air Inlet Node" is the name of the 
node at the mixer's OA inlet.

  Output:Variable,
    Outside Air Inlet Node,  !- Key Value
    System Node MassFlowRate,!- Variable Name
    timestep;                !- Reporting Frequency

Jan Lima wrote:
>
>
> Hi
>  
> I am simulating an Air Handling Unit with recirculation and outside 
> air, but I can't insert outside air. I've  checked the svg file and 
> the system is recirculating all air(zone air) with the outside air 
> node disconneted. Besides, the Object CONTROLLER: OUTSIDE AIR is not 
> working. I've already checked the example file 
> 5ZoneBoilerOutsideAirReset and it also has the same trouble - the 
> outside air node is disconnected. Do you have any suggestions?
>  
> Jan Lima
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/