[EnergyPlus_Support] Re:Controller:MechanicalVentilation



You can try at Controller:MechanicalVentilation object:

1. Set field 'Zone Outdoor Air Method' to Maximum and set cfm/ft2 to 0 
for zones.

2. Set field 'System Outdoor Air Method' to ZoneSum as you indicated. 
You can ignore zone distribution effectiveness and system ventilation 
efficiency inputs.

Unfortunately you have to enter outdoor air rates at the 
Controller:MechanicalVentilation object in order to model DCV. Currently 
the outdoor air rates in the autosizing calculations are different from 
the annual simulations for DCV. A plan is in place to consolidate these 
inputs for both objects.

Tianzhen



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/