You can try at Controller:MechanicalVentilation object:
1. Set field 'Zone Outdoor Air Method' to Maximum and set cfm/ft2 to 0
for zones.
2. Set field 'System Outdoor Air Method' to ZoneSum as you indicated.
You can ignore zone distribution effectiveness and system ventilation
efficiency inputs.
Unfortunately you have to enter outdoor air rates at the
Controller:MechanicalVentilation object in order to model DCV. Currently
the outdoor air rates in the autosizing calculations are different from
the annual simulations for DCV. A plan is in place to consolidate these
inputs for both objects.
Tianzhen
__._,_.___
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___