[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] model VRF system



I think the closest you could get on the cooling side would be to use an 
AirloopHVAC:UnitaryCoolOnly with AirTerminal:SingleDuct:VAV:NoReheat air 
distribution units. The power side of the VRF would have to be modeled 
using a squared curve on PLR where Power is proportional to the square 
of speed (or PLR). However, with this configuration the fan power will 
be low since VRF systems typically use constant volume fans. You can 
modify the fan power in a spreadsheet after the simulation is complete. 
Sorry if the jpg doesn't come through but it just shows the squared 
power law of power vs speed..

For heating it is much harder. Using the 
AirloopHVAC:UnitaryHeatPump:AirToAir with 
AirTerminal:SingleDuct:Uncontrolled will model both cooling and heating, 
however, the compressor control is limited to a single zone. If the zone 
loads are balanced (flow through air distribution units are balanced 
based on load) this will be a fair approximation, at least with what is 
available in EnergyPlus. You could still use the squared curve for power 
in this object.

So there is no simple answer, you would have to pick a system and review 
the results to see how close you are to manufacturers performance data. 
Then modify the input to more closely model the system using different 
configurations. There are many EnergyPlus users that would be interested 
in your findings.

VRFPower.jpg

mohammd al masri wrote:
>
>
> Dear all,
> I have a VRF (variable refrigerant flow) system , how I can model it ?
> can I use something closeor similar to that system , some mechanical 
> engineers tolds me to select cooling tower system .
>  
> Any help,
> Thanx
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
Attachment not found:
d:\eudora\attach\VRFPower.jpg