Hello Dashamir,

If you have the Maximum Water Flow or Maximum Hot Water Flow set to autosize, I believe those objects will require a Sizing:Zone as this is what happens when I try to autosize my DXSingleCooling speed flow rate.

Arslan
coop Student
greenAdvance Inc.

On Wed, Jun 17, 2009 at 9:31 AM, dashamir marini <dashamirmarini@xxxxxxxxx> wrote:



hi all

I have modeled one system using only radiant panels as zone equipment (there is no any air flow network for heating and cooling). The only air flow network used in model is applied for zone infiltration. When I run model with sizing zone object it run correctly, when remove this object (sizing zone) at HVAC Design list I got this error:

** Severe  ** For autosizing of ZoneHVAC:LowTemperatureRadiant:VariableFlow APP_O_1 RADIANT FLOOR, a zone sizing run must be done.
   **   ~~~   ** No "Sizing:Zone" objects were entered.
   **  Fatal  ** Program terminates due to previously shown condition(s).
   ...Summary of Errors that led to program termination:

From in/out I read that this object provide the data needed to perform zone design air flow calculation (whil e in my case is only radiant panel).

is there any connection between zone infiltration and sizing zone objects ?
from wat is caused this error ?

thanks in advance....






--
Arslan Djumaev,
Architectural R&D Engineer
greenAdvance Inc.
605 Northgate Ave.
Waterloo, ON N2L4R1
Cell: (519) 721 5392
www.greenadvance.ca

Confidentiality Warning: This e-mail contains information intended only for the use of the individual or entity named above. If the reader of this e-mail is not the intended recipient or the employee or agent responsible for delivering it to the intended recipient, any dissemination, publication or copying of this e-mail is strictly prohibited.


__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___