Re: [EnergyPlus_Support] Re: winter design day





Just look at the object: SizingPeriod:DesignDay.

Not sure what you mean by difficulties during simulation.  Take as a guide ones that are included with the installation or check out others that are available for download.

(See the Locations-Designdays spreadsheet in the MacroDataSets folder that is under the main install (root) folder.

These usually specify the design days as outlined by ASHRAE.

For example,
titles with:  Heating 99% Design Conditions DB mean they are the 99% for heating (only 1% of the time will the conditions exceed that) with the DB meaning they are based on Dry Bulb Temperature.

Cooling has many more options (again outlined when you use which in ASHRAE HOF).  Cooling DB=>MWB 1% in the title is saying Dry Bulb with a Mean Wet Bulb -- often used for cooling design but other buildings will need different conditions.


At 04:00 PM 6/24/2009, Sajal Chowdhuri wrote:


if i can make my own design day profile then it may occur many difficulties while simulation.how can we generate our own design day,have any specification?
thanks

From: Linda Lawrie <linda@xxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thursday, June 25, 2009 2:43:36 AM
Subject: Re: [EnergyPlus_Support] Re: winter design day

Feel free to make up your own design day profiles.

You asked why the ones supplied were a certain way and Jim answered.  That you don't agree is a mute point.

EnergyPlus Development Team






__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___