Thanks, Dru
For providing the ASHRAE reference.
Actually the original poster has given his own answer by quoting. "Note that usual Winter design conditions are for very cloudy days The fixed outdoor temperature for the 24 hour period does not mean that the heating load change of the building is also zero. There are other variables in the simulation.
I use the DesignDay simulation all the time, because I am the only person in this group still using a slow Pentium I, WindowsME PC.
In addition to the heating and cooling load sizing, I also use it to verify the correct expansion of the schedules and the use of temperature setpoints, and to verify the People, lights on weekdays, holidays, etc. are correctly calculated. It is so simple to get the 24 outdoor temperature numbers by changing only two numbers (Max. and range.) Of course, you can enter zero for SummerDesignDay as well. It will happen on a rainy day.
For places like Malaysia, Singapore and HongKong, there is no snow cover nor severe Winter. My WinterDesignDay is a rainy cloudy day. It is very flexible and convenient to change and use.
So feel free to change the field values, and observe the effects and make the most of it.
Of course, if you are submitting an energy Green Star report, for example, you need to follow the ASHRAE standard. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: Drury.Crawley@xxxxxxxxxx Date: Thu, 25 Jun 2009 11:16:35 -0400 Subject: RE: [EnergyPlus_Support] Re: winter design day Jerry,
ASHRAE Technical Committee (TC) 4.2 Climatic Information developed the design day concept, working with TC 4.1 Load Calculations as a way to calculate the peak heating and cooling load conditions. (Sorry if I'm repeating subsequent discussion..
The 0.4%, 99.6% represent the number of hours in a year that you could reasonably expect a particular temperature to be exceeded. This is calculated from the most recent 20-30 years of weather for that location. The ASHRAE Fundamentals Handbook--which is our primary source of data--also have the most extreme conditions.
These design conditions are simply used to size the heating and cooling equipment. The hourly weather data is what is used by EnergyPlus to calculate the operating energy performance of the building.
Hope I haven't confused the issue more.
Dru Crawley DOE From: EnergyPlus_Support@ Sent: Wednesday, June 24, 2009 5:36 PM To: EnergyPlus_Support@ Subject: Re: [EnergyPlus_ Thanks for the quick reply, but to be honest I'm still not convinced. If a Windows Live helps you keep up with all your friends, in one place. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.