Re: [EnergyPlus_Support] Outward Facing Angle for a subsurface



If you look at the first 3 points in the BuildingSurface:Detailed 
object, they are described opposite in direction to the fenestration 
coordinates which may be confusing E+. I'm not sure of this, but you 
could also try using point 3 as the first point in the list where point 
1 and 2 would be listed last. You could also try splitting up the 
surface into 2 or more surfaces where the fenestration surface is 
"within" the boundary of a 4-point surface.

philcook76 wrote:
>
>
> I am trying to model a building with a sawtooth roof. I have drawn the 
> model in SketchUp but when I run the IDF file with EPlus Launch, I get 
> the error:
> ** Severe ** GetSurfaces: Outward facing angle [90.0] of 
> subsurface="ZNWARE:E_WALL:ROLLER_DOOR" significantly different than
> ** ~~~ ** ..facing angle [270.0] of base surface=ZNWARE:E_WALL Tilt=90.0
> ** ~~~ ** ..surface class of base surface=Wall
>
> Both of the surfaces are described anticlockwise when looking at them 
> from outside the building. I have included the extracts from the IDF 
> file for these surfaces below. I have tried to redraw them several 
> times but with the same results. Is this an E+ problem or something to 
> do with OpenStudio?
>
> Thanks,
> Phil
>
> BuildingSurface:Detailed,
> ZnWare:E_Wall, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> WarehouseZone, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 8, !- Number of Vertices
> 65.000000, 65.646926, 10.700000, !- X,Y,Z 1 {m}
> 65.000000, 65.646926, 8.000000, !- X,Y,Z 2 {m}
> 65.000000, 65.000000, 8.373503, !- X,Y,Z 3 {m}
> 65.000000, 65.000000, 0.000000, !- X,Y,Z 4 {m}
> 65.000000, 75.000000, 0.000000, !- X,Y,Z 5 {m}
> 65.000000, 75.000000, 8.000000, !- X,Y,Z 6 {m}
> 65.000000, 70.323463, 10.700000, !- X,Y,Z 7 {m}
> 65.000000, 70.323463, 8.000000; !- X,Y,Z 8 {m}
>
> FenestrationSurface:Detailed,
> ZnWare:E_Wall:Roller_Door, !- Name
> Door, !- Surface Type
> Exterior Roller Door, !- Construction Name
> ZnWare:E_Wall, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 65.000000, 66.106057, 6.000000, !- X,Y,Z 1 {m}
> 65.000000, 66.106057, 0.000000, !- X,Y,Z 2 {m}
> 65.000000, 74.106057, 0.000000, !- X,Y,Z 3 {m}
> 65.000000, 74.106057, 6.000000; !- X,Y,Z 4 {m}
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/