Re: [EnergyPlus_Support] fan:zone:exhaust // infiltration



Camille,

The exhaust fan will not do what you want: exhaust air and induce an 
balancing amount of
infiltration.

I know it sounds weird, but the best way of doing what you want is to 
use the ZoneVentilation
object.

Fred Buhl

le_carambar wrote:
> Hi,
>
> I work on a building with a simple air extraction system. Air is replaced thanks to infiltration. 
>
> I think I should use Fan:Zone:Exhaust and ZoneInfiltration:DesignFlowRate objects. 
>
> My probleme is that I can't choice the flow rate in the exhaust fan, only the pressure rise and the maximum flow rate.
>
> So, I'm not sure that the airflows are equilibrated.
>
> Can you help me ?
>
> Thanks,
>
> Camille T.
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/