Re: [EnergyPlus_Support] Re: Outward Facing Angle for a subsurface
This one might be because the lowest coordinates of the door (0.000000)
is the same as the wall. The door is not "enclosed" by the wall. Try
making the lowest door coordinate (0.000001). You might have to raise
the door as high a 1 mm (0.001) to make this work. You can also raise
the top of the door to keep the same dimension. As in the last email,
you can split up the surface into 2 or more surfaces so that the door is
within a 4-point surface. And yes, you can ignore this warning but it is
always better to eliminate all warnings.
FenestrationSurface
:Detailed,
ZnWare:E_Wall:Roller_Door, !- Name
Door, !- Surface Type
Exterior Roller Door, !- Construction Name
ZnWare:E_Wall, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
65.000000, 66.106057, 6.000000, !- X,Y,Z 1 {m}
65.000000, 66.106057, 0.000001, !- X,Y,Z 2 {m}
65.000000, 74.106057, 0.000001, !- X,Y,Z 3 {m}
65.000000, 74.106057, 6.000000; !- X,Y,Z 4 {m}
-OR-
65.000000, 66.106057, 6.001, !- X,Y,Z 1 {m}
65.000000, 66.106057, 0.001, !- X,Y,Z 2 {m}
65.000000, 74.106057, 0.001, !- X,Y,Z 3 {m}
65.000000, 74.106057, 6.001; !- X,Y,Z 4 {m}
philcook76 wrote:
>
>
> Thanks a lot Richard. You were exactly right. I moved the first two
> points to the end of the list and the problems stopped.
>
> Now I am getting a warning that the doors contained within a wall are
> not fully enclosed. Should I just ignore this warning? I have enclosed
> a relevant extract from the IDF file.
>
> Phil
>
> BuildingSurface:Detailed,
> ZnWare:E_Wall, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> WarehouseZone, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 8, !- Number of Vertices
> 65.000000, 65.000000, 8.373503, !- X,Y,Z 3 {m}
> 65.000000, 65.000000, 0.000000, !- X,Y,Z 4 {m}
> 65.000000, 75.000000, 0.000000, !- X,Y,Z 5 {m}
> 65.000000, 75.000000, 8.000000, !- X,Y,Z 6 {m}
> 65.000000, 70.323463, 10.700000, !- X,Y,Z 7 {m}
> 65.000000, 70.323463, 8.000000, !- X,Y,Z 8 {m}
> 65.000000, 65.646926, 10.700000, !- X,Y,Z 1 {m}
> 65.000000, 65.646926, 8.000000; !- X,Y,Z 2 {m}
>
> FenestrationSurface:Detailed,
> ZnWare:E_Wall:Roller_Door, !- Name
> Door, !- Surface Type
> Exterior Roller Door, !- Construction Name
> ZnWare:E_Wall, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 65.000000, 66.106057, 6.000000, !- X,Y,Z 1 {m}
> 65.000000, 66.106057, 0.000000, !- X,Y,Z 2 {m}
> 65.000000, 74.106057, 0.000000, !- X,Y,Z 3 {m}
> 65.000000, 74.106057, 6.000000; !- X,Y,Z 4 {m}
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> <RRaustad@...> wrote:
> >
> > If you look at the first 3 points in the BuildingSurface:Detailed
> > object, they are described opposite in direction to the fenestration
> > coordinates which may be confusing E+. I'm not sure of this, but you
> > could also try using point 3 as the first point in the list where point
> > 1 and 2 would be listed last. You could also try splitting up the
> > surface into 2 or more surfaces where the fenestration surface is
> > "within" the boundary of a 4-point surface.
> >
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/