Re: [EnergyPlus_Support] Output analysis : Zone Air Balance Surface Convection Rate



I should have also told you that convection from window frames and 
dividers ARE ALSO included in the Zone Air Balance Surface Convection 
Rate report variable (but not the glazing). So the comparison you are 
making would not add up exactly if window frames and dividers are used. 
If there are no window frames or dividers (or no windows at all), I 
would think the numbers should match.

Richard Raustad wrote:
>
>
> If you want to know the definition of any report variable, search for it
> in the Input Output Reference document. Here is what I found:
>
> The Zone Air Balance Surface Convection Rate is the sum, in watts, of
> heat transferred to the zone air from all the surfaces. This field is
> not multiplied by zone or group multipliers.
>
> I don't think that Window Convection Heat Gain from Glazing to Zone is
> included in the Zone Air Balance Surface Convection Rate. Leave the
> glazing gain out and see if the numbers match up better.
>
> le_carambar wrote:
> >
> >
> > Dear users,
> >
> > I try to understand what is include in the output variable : Zone Air
> > Balance Surface Convection Rate.
> >
> > I did the sum of the "Surface Int Convection Heat Rate" for every
> > surfaces (1 ext wall, 3 interzone surfaces, 1 roof, 1 floor) and
> > "Window Convection Heat Gainfrom Glazing to Zone". And the result is
> > not the same value than "Zone Air Balance Surface Convection Rate".
> >
> > I check output variable "Window Gap Convective Heat Flow" and "Window
> > Convection Heat Gain from Gap between Shade and Glazing to Zone " but
> > they are equal to 0.
> >
> > Can you help me ?
> >
> > thanks,
> >
> > Camille T.
> >
> >
>
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/