I assumed the ACH at 50 pascals would apply towards infiltration.
The infiltration object is called "ZoneInfiltration:DesignFlowRate"

In an AirlfowNetwork simulation, this infiltration object is not used.
Instead the flow pressure relationship is defined

Q= c DeltaP ^n and assuming n=0.65

Since you know Q, DeltaP and n, you can back calculate c with your data.

Read the documentation for AirflowNetwork in the IO Ref and Eng Ref.


v s wrote:
>
>
> How can i enter this imformation to E+?
> In the "natural ventilation and duct leakage", at "airflownetwork 
> multizone component detailed opening"
> how can i define the "air mass flow coefficient when opening is closed"?
> If i suppose that i have 0.001 kg/sec/m of opening, should i put this 
> number there?
> Because the difference between the factors 40 and 20 is large, since i 
> cannot find the exact factor for my place, Greece.
>
> Thank you Richard.
>
> If you know the ACH at 50 pascals, you need to convert that information
> to the ACH at normal building pressure. Here in Florida we use a factor
> of 40 (which would mean ACH = 0.025 at normal building pressure), in the
> rest of the United States the factor is 20 (which would mean ACH =
> 0.05). The different factors represent the differences in altitude,
> local average wind speed, stack effect, etc. So in Florida, 2.5% of the
> total building volume is exchanged each hour (m3/hr) and then that
> number would have to be converted to m3/s (divide by 3600).
>
> There are tables in the Residential Energy book by Krigger (pg 286 in
> the appendix) that specify the factors used for other locations, but for
> other countries, I am not sure where that information would be found.
>
> v s wrote:
> >
> >
> > Dear all.,
> >
> > I want to have an input for infiltration 1ACH for a pressure of 50
> > Pascal (n50).
> > How this can be done?
> >
> > Thanks
> > vaggelis
> >
> > ------------ --------- --------- --------- --------- --------- -
> > *From:* Richard Raustad <RRaustad@FSEC. UCF.EDU 
> <mailto:RRaustad%40FSEC.UCF.EDU>>
> > *To:* EnergyPlus_Support@ yahoogroups. com 
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > *Sent:* Friday, July 10, 2009 4:11:10 PM
> > *Subject:* Re: [EnergyPlus_ Support] Output analysis : Zone Air Balance
> > Surface Convection Rate
> >
> > If you want to know the definition of any report variable, search for it
> > in the Input Output Reference document. Here is what I found:
> >
> > The Zone Air Balance Surface Convection Rate is the sum, in watts, of
> > heat transferred to the zone air from all the surfaces. This field is
> > not multiplied by zone or group multipliers.
> >
> > I don't think that Window Convection Heat Gain from Glazing to Zone is
> > included in the Zone Air Balance Surface Convection Rate. Leave the
> > glazing gain out and see if the numbers match up better.
> >
> > le_carambar wrote:
> > >
> > >
> > > Dear users,
> > >
> > > I try to understand what is include in the output variable : Zone Air
> > > Balance Surface Convection Rate.
> > >
> > > I did the sum of the "Surface Int Convection Heat Rate" for every
> > > surfaces (1 ext wall, 3 interzone surfaces, 1 roof, 1 floor) and
> > > "Window Convection Heat Gainfrom Glazing to Zone". And the result is
> > > not the same value than "Zone Air Balance Surface Convection Rate".
> > >
> > > I check output variable "Window Gap Convective Heat Flow" and "Window
> > > Convection Heat Gain from Gap between Shade and Glazing to Zone " but
> > > they are equal to 0.
> > >
> > > Can you help me ?
> > >
> > > thanks,
> > >
> > > Camille T.
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec. ucf.edu <http://ucf.edu> 
> <http://www.fsec. ucf.edu <http://www.fsec.ucf.edu>>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
>
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec. ucf.edu <http://www.fsec.ucf.edu>
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/