Som: Asked same question of E+ help desk several months back.
Here’s the response I got… The mass flow rates (kg/s) are used in internal
calculations in the AirflowNetwork model. The volume flow rates are used for
report only and mainly designated for multizone airflows and not for airflows
in an air distribution system. They are calculated by dividing the mass flow
rates by the outdoor air density for multizone airflow rates and zeros for
distribution links. I will make changes for the next release. Thanks for
bringing this issue. Lixing Dave -- David R. Roberts, P.E. Senior Engineer Residential Buildings Group Electricity, Resources & Building Systems Integration Center National Renewable Energy Laboratory (NREL) 303.384.7496 From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of somsgr I am using AirflowNetwork to estimate duct heat
gain/loss and airflow through each duct section. I got reasonable output for
"AirflowNetwork Mass Flow Rate from Node 1 to 2", but the
"AirflowNetwork Volume Flow Rate from Node 1 to 2" is zero for the
same link (for all links). I appreciate any suggestion to fix the issue. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.