| Hi Natassa I would like to say that is not so easy to realise that connection equipment, but not impossible. Refering your error, I think that you may have input for the same node two different in/out node connection. FancoilAirOutletNode, have to be the same node for ZoneAirInletNode, and by otherside ZoneAirExhaustNode have to be the same node for FancoilAirInletNode. Those nodes are input in some object: ZoneHVAC EquipmentConnections (Zone Air Inlet/Exhoust Nodes) which those Nodes are also input at Node-Branch Mannagement group Object: Node list also the samme nodes are inpot in ZoneHVAC:FourPipeFanCoil object. For more detail you can see : FanCoilAutoSize idf file at examples file. good luck best regards Dashamir __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.