[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Heat recovery warning



I'm not sure if manufacturers don't recommend operating outside of this 
range... I think its more that we are linearly extrapolating performance 
data measured at 75% flow and 100% flow... and if you extrapolate beyond 
50% and 130% that linear assumption probably doesn't hold.



Richard Raustad wrote:
> Report the supply (primary) and exhaust (secondary) air streams mass 
> flow rate using the output variable report below.
>
> Output:Variable,
> *,
> System Node MassFlowRate,
> TimeStep;
>
> Substitute the nodes name for the HX's supply and exhaust air streams 
> for the * above.
>
> Then compare the average of these 2 values with the nominal HX supply 
> air flow rate specified in the 
> HeatExchanger:AirToAir:SensibleAndLatent object (named AHU HEAT 
> RECOVERY).
>
> You should see that the average is out of range. The manufacturers do 
> not recommend operating outside the range of <50% or >130%.
>
> You could also change the type of HX, there is a sensible only flat 
> plate model that does not have this restriction (if you do not need 
> total heat recovery).
>
> johnnyklemke wrote:
>>  
>>
>> Hi all,
>>
>> I've been running a model with ASHRAE system 8 (VAV with heat 
>> recovery) and could not solve a warning with the heat recovery 
>> component:
>>
>> HeatExchanger:AirToAir:SensibleAndLatent "AHU HEAT RECOVERY"
>> ** ~~~ ** Average air volume flow rate is <50% or >130% of the 
>> nominal HX supply air volume flow rate.
>> ** ~~~ ** Air volume flow rate ratio = 7.454E-002. Occurrence 
>> info=SAO_PAULO/CONGONHAS - BRA TMY3-837800 WMO#=837800, 01/02 06:00 - 
>> 06:10
>>
>> ===== Recurring Error Summary =====
>> ************* The following recurring error messages occurred.
>> *************
>> ************* ** Warning ** HeatExchanger:AirToAir:SensibleAndLatent 
>> "AHU HEAT RECOVERY": Average air volume flow rate is <50% or >130% 
>> warning continues. Air flow rate ratio statistics follow.
>> ************* ** ~~~ ** This error occurred 999249 times.
>> ************* ** ~~~ ** Max=0.499985 Min=7.383128E-002
>>
>> Can anyone help me on this? How can I solve this issue? I don't know 
>> how to measure this 50/130% of average air volume flow rate.
>>
>> Thanks,
>> John
>>
>> 
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/