[EnergyPlus_Support] Re: Appropriate setpoints for shading device schedule



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jkneifel_florida" <jkneifel_florida@...> wrote:
>
> I would like to create a schedule to control shades in a building, but I have not been able to find any information on the appropriate setpoint to determine when there is "high solar" on the window surface. Is there a recommended W/m2 during summer months to decrease cooling loads? Thanks in advance.
>
An optimum setpoint for shading control really depends on a number of factors including the glazing percentage and the quality (g-value) of the glazing. For low glazing percentages the setpoint can be higher 300-350 W/m2. For high glazing percentages perhaps as low as 100-150 W/m2. 200 W/m2 might be a good start.



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/