FW: [EnergyPlus_Support] Re: *.Rvi File Question





Tobias,
 
It's fairly simple.. RVIs and MVIs a set of text files that you can edit with Notepad (they are described in the InputOutput Reference). An RVI (or MVI) starts with the name of the .ESO file (by default, while running E+ -- eplusout.eso) and the name of the output file (defaults to eplusout.csv).  It then has a list of output variables (in the RVI) or meter names (in the MVI).  The last line is a 0.  There are several examples in the ExampleFiles directory.  By default, it is assumed that you have a single RVI or MVI.  But you can create your own to specific parts of the buildings.  A recent set of run I did had 17 different RVIs such as Windows, Envelope, Solar Gains, Zone Conditions, etc.  That made it easier to look at the data in Excel. I created a separate batch file but below is an example of how you might edit the Epl-run.bat (which EP-Launch uses).
 
First, to figure out which variables are applicable to your simulation, add (or make sure you already have) this line to your IDF (or edit it in IDF Editor):
 
Output:VariableDictionary,IDF,Unsorted;
 
When you run your simulation, you'll have a new file (if you didn't already) with the extension of .RDD.  If you use the form above (IDF), then the variables will already be in IDF format. You can then just cut and paste the variables you want from the RDD to your IDF (in Notepad or IDF Editor).
 
Next you can edit (with Notepad), the file called Epl-run.bat to include your RVIs, it will automatically run them when you use EP-Launch.
 
You would need to add lines in Section 6 similar to:
 
IF EXIST eplusout.inp postprocess\ReadVarsESO.exe eplusout.inp %rvset%
IF NOT EXIST eplusout.inp postprocess\ReadVarsESO.exe " " %rvset%
IF EXIST eplusmtr.inp postprocess\ReadVarsESO.exe eplusmtr.inp %rvset%
IF NOT EXIST eplusmtr.inp echo eplusout.mtr >test.mvi
IF NOT EXIST eplusmtr.inp echo eplusmtr.csv >>test.mvi
IF NOT EXIST eplusmtr.inp postprocess\ReadVarsESO.exe test.mvi %rvset%
 
For example, say I had an RVI on solar gains called SolarGains.RVI and a MVI on lighting meters called LightingMeter.RVI.  So I could add to the lines above:
 
IF EXIST eplusout.inp postprocess\ReadVarsESO.exe eplusout.inp SolarGains.RVI
IF EXIST eplusmtr.inp postprocess\ReadVarsESO.exe eplusmtr.inp LightingMeter.MVI
 
You will probably also have to add a line renaming the output from the ReadVarsESO... something along the lines of:
IF EXIST eplusout.csv MOVE eplusout.csv "%output_path%%1SolarGains.csv"
 
 
 



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of tobias.leibing
Sent: Tuesday, October 27, 2009 8:26 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: *.Rvi File Question

 

Hey there,

I was looking also for that exact thing and managed now to at least create one RVI-file that pulls the defined variables in the CSV-file.
However, since I am not really familiar with software programming topics like this 'batch-file' that, as I learned now, apparently is need for multiple RVI-/CSV-files.
I was looking into the installation folder of E+ and found several batch-files (Epl-run, RUNEP, RunEPlus, RunReadEso) which are editable with the notepad.

Can anybody please help me with the modifications of those and also, how it works exactly with creating multiple RVI-files. I already tried to give the one file a different name but then the CSV-file didn't come out after the simulation.

Thank you for your assistance,
Tobias

--- In EnergyPlus_Support@yahoogroups.com, "Crawley, Drury" <Drury.Crawley@...> wrote:
>
> Mike,
>
> I'm doing exactly that--creating individual RVIs for different outputs
> and meter results. It's fairly simple to create a modified batch file to
> run this--after the simulation is completed. I can share my modified
> batch file if you're interested. I have about 20 separate RVIs and MVIs
> (of course tailored to the IDFs I'm running).
>
> Dru
>
> ________________________________
>
> From: EnergyPlus_Support@yahoogroups.com
> [mailto:EnergyPlus_Support@yahoogroups.com] On Behalf Of Micheal
> Sent: Friday, July 06, 2007 4:07 PM
> To: EnergyPlus_Support@yahoogroups.com
> Subject: [EnergyPlus_Support] Re: *.Rvi File Question
>
>
>
> Thank for the quick response. I thought this would be the case.
>
> I have a follow-up question. Can you run RunReadvarsESO.exe multiple
> times? For example have several RVI files with "sets" of variables
> like environment, walls, zones, systems and report to multiple *.csv
> files. Also could use separate time frames in the *.rvi files. Using
> this methodology I would hope I could import the various *.csv sets
> into excel on different worksheets and use the data to create
> reports in my own format.
>
> A second question is do you know what happens if the *.rvi variable
> is not present? For example if I where to enforce a generic naming
> convention (such as wall1, wall2, ...) and not use all the names.
> Would I just get the warning "The following variable were requested
> but not generated". Do you know if it would "skip" the column to
> maintain an absolute relationship or delete the non-existent
> variable column to create a compact table with no "empty" columns?
>
> Thanks in advance,
>
> Mike
>
> PS: I have and use XESOView which I find to be a very good program.
> The problem I run into is that it doesn't allow looking at (charting
> or reporting) multiple variables at the same time. Also, the company
> I work for has quite a few "oldtimers" which I need to produce
> outputs formatted in similar ways to their currently used methods
> (CHVAC, Trace, and even hand calculated CLTD!) so that they can
> better understand what is going on. The buildings we tend to model
> are simple and very similar to one another (warehouses, maintenance
> buildings, mechanical buildings, etc. for electric power plants). I
> plan on masking most of the input and output of EPlus in a
> more "user friendly" format using Excel hense all the questions
> above.
>
> --- In EnergyPlus_Support@yahoogroups.com
> <mailto:EnergyPlus_Support%40yahoogroups.com> , Linda Lawrie
> <lklawrie@> wrote:
> >
> > You must use the rvi file for this purpose. Whatever you put in
> > report variables, get shoved out to the eso file (or in case of
> > meters also the .mtr file) as they "come up" in the simulation.
> The
> > actual order for that would be shown in the first part of the eso
> > file (before the part that says "End of Data Dictionary".
> >
> > In the rvi file, you can either specify the generic form of the
> > report variable, e.g.:
> >
> > Zone/Sys Air Temperature
> > Zone/Sys Sensible Heating Energy
> > Zone/Sys Sensible Cooling Energy
> >
> > or be really specific:
> > Zone 1:Zone/Sys Air Temperature
> > Zone 1:Zone/Sys Sensible Heating Energy
> > Zone 1:Zone/Sys Sensible Cooling Energy
> >
> > The first instance will give you all the zones, Zone/Sys Air
> > Temperature, followed by all the Zones, Zone/Sys Sensible Heating
> > Energy, etc. whereas the second will put the 3 variables by zone.
> >
> > There are also ways of only getting out the hourly or monthly
> values
> > in a csv file even though the eso file may contain multiple hourly
> > and monthly mixed.
> >
> > There is also the utility XESOView (not part of the EnergyPlus
> > install) but you can find out about it on either the yahoo groups
> > website or the energyplus.gov website. I don't know if it would
> be
> > suitable for your purposes or not.
> >
> >
> > Linda
> >
> > EnergyPlus WebSite: http://www.energyplus.gov
> <http://www.energyplus.gov>
> > Owner: EnergyPlus_Support list
> > Member: EnergyPlus Development Team
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
>
>
>
>
>
> [Non-text portions of this message have been removed]
>



__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___